Anonymous Poster

ALUMINIUM BUSBAR SIZE

08/27/2009 12:27 AM

I HAVE A 3 PHASE ALTERNATOR OF 320 KVA RATING. I WANT ALUMINIUM BUSBAR SIZE FOR LOAD DISTRIBUTION. LOAD CABLE IS 240 MM SQUARE ALUMINIUM.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: ALUMINIUM BUSBAR SIZE

08/27/2009 12:39 AM

Please restate your demand in the form of a question, and DO NOT use capital letters.

Reply
Guru

Join Date: Apr 2007
Posts: 577
Good Answers: 10
#2

Re: ALUMINIUM BUSBAR SIZE

08/27/2009 2:00 AM

Please give more information. What is the rated Voltage 380V, 415V, 420V, 440V or 480V.

__________________
Management is just like a bunch of Monkey sitting on a tall tree. Some climb to the highest branch and some at the lowest branch. The highest Monkey look down and see a lot of happy faces but the lower Monkey looks up and see nothing but all the....
Reply
Member

Join Date: Aug 2009
Posts: 7
#4

Re: ALUMINIUM BUSBAR SIZE

08/27/2009 3:30 AM

The information provided by you is insufficent,

pls provide more detail like voltage level etc

Reply
Active Contributor

Join Date: Jan 2008
Posts: 18
#5

Re: ALUMINIUM BUSBAR SIZE

08/27/2009 7:34 AM

If I understand , your question you want to put aluminium bus bar in place of power cable . Presently u are using 240 sq mm Aluminium cable.

So for 320 KVA however we need Voltage also but if I assume your Alternator is designed for 415 Volts in that case 320 KVA load would be around 556 Amps with Power factor of 0.8 lagging.

so for 556 amps current you need 15 X 2.5 mm size Flat rectangular Bus bar this can take 562 amps load and considering load type you need to design higher side so go for 20 X 4 mm size falt Rectangular Bus Bar.

Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#6

Re: ALUMINIUM BUSBAR SIZE

08/27/2009 4:25 PM

You have not supplied nearly enough information for us to answer your loud, vague and potentially dangerous application.

Please see the numerous previous threads on CR4 on the subject, or alternatively get a professional to design and wire your alternator.