Tapping of Orifice Plates

09/12/2009 8:34 AM

Hi,

In flow measuring using Orifice plates if I decided to change type of tapping from flange tapping to vena contracta tapping (as an Example) would it affect the my readings of flow? and why?

What do I mean is that does the dimensions of the upstream and downstream tapping points affect the flow reading?!

Regards,,,

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Brazil - Member - New Member Engineering Fields - Mechanical Engineering - New Member Hobbies - RC Aircraft - New Member Hobbies - Target Shooting - New Member Hobbies - Automotive Performance - Hey there... interested in exchanging information about car performance? Hobbies - DIY Welding - New Member

Join Date: Jan 2007
Location: Porto Alegre - RS - Brazil 30deg01'39.73"S 51deg13'43.45"W
Posts: 831
Good Answers: 28
#1

Re: tapping of orifice plates

09/12/2009 8:41 AM

There are some differences in calculations as long as I remember. Refer to ISO 5167 for the proper procedures.

__________________
Humm... suspicious you are...
Reply
Active Contributor

Join Date: Jul 2009
Location: Chennai
Posts: 11
#2

Re: Tapping of Orifice Plates

09/13/2009 11:25 AM

Hi,

Yes definitely,as there is a change in the cross section of the pipe.i.e in the vena contracta area is the area of minimum cross section further after vena contracta the fluid coming out expands to fill in the pipe,further in case of orifice meter there will be abrupt change in the cross section after vena contracta..

Hope it is useful!!!!

Rgds

Arun

Reply
Power-User

Join Date: Mar 2008
Location: Houston, Texas
Posts: 101
Good Answers: 6
#3

Re: Tapping of Orifice Plates

09/14/2009 10:26 AM

It would affect the reading,because you sized based on flange tapping and calibrated the transmitter accordingly.

Now if you change the tapping to vena contracta ,for the same flow, the differential pressure measured is different for flange tapping and vena contracta tapping.

See ISO or MPMS standard and you will see different discharge co-efficient for flange,vena contracta, and D and D/2 tappings

__________________
If you don't know where you are going,you are bound to get there
Reply
Commentator

Join Date: Mar 2009
Posts: 61
Good Answers: 3
#4

Re: Tapping of Orifice Plates

09/17/2009 9:08 AM

Orifice flange taps facilitate pressure sensing immediately before and after the orifice plate, because the vena-contractor does not occur immediately at the outlet of the orifice plate the differential pressures measured for particular flow rates will vary from flange tapped installations.

Regarding the second question; the further downstream you go from the orifice plate the closer measured pressure will be to it's optimum value (i.e. upstream pressure - irrecoverable pressure loss which is inherrent with all differential pressure type flow elements). This means that the measurable dp range for particular flows will be less than flange taps, therefore the calibrated dp range of the transmitter will need to be adjusted accordingly. This can have adverse effects on accuracy of the flow indication.

Reply
Commentator
India - Member - ADIL MOULA Engineering Fields - Instrumentation Engineering - Adil Moula

Join Date: Jun 2008
Location: India
Posts: 95
Good Answers: 1
#5

Re: Tapping of Orifice Plates

09/22/2009 4:50 PM

As per standards( ref: handbook of petroleum and natural gas engineering vol-2 pg 803)

Flange taps are located 1in upstream and 1inch down stream of the orifice .

Pipe taps are 2.5 times ID for upstream and 8 pipe ID for down stream.

Venacontracta taps are one ID upstream and down stream is located at plane of vena contracta.

Corner taps located immediately adjacent to upstream and down stream faces of the orifice .

from above standards we can see that all taps are not located at same plane of vena contracta hence your reading should differ ,if the taps are only changed .

Reply
Anonymous Poster
#6

Re: Tapping of Orifice Plates

10/06/2009 11:41 PM

please till me the toleranc of tapping angle at orifice flange