Re: how to test single phase isolation transformer
09/15/2009 7:54 AM
You can get an idea by using a PAT (Portable Appliance Test) tester to check for leakage between the primary and secondary, but this will only use (typically) 500Vdc. You will need an insulation tester (e.g. a "Megger") or high voltage generator to produce the 1.5kV, 5kV (or whatever the specification says) to do a proper proof test.
__________________
"Love justice, you who rule the world" - Dante Alighieri
Re: how to test single phase isolation transformer
09/16/2009 6:36 AM
You need to check leakage current from primary to ground, primary to secondary and secondary to ground all with the transformer disconnected from supply and load, and with a DC (NOT AC) test voltage.
The 25V earth to neutral that you're measuring (which is AC) tells you little, if anything, about the isolation.