PC Problems: Smoking UPS

09/17/2009 1:17 AM

Sir,

Smoke came out from ac power entry side in my PC's UPS (APC 500VA, 2005/06) 3-4 days back with burning smell while there was a sudden power failure in our locality in Shillong. I got it repaired and it worked nicely in his room, but, again develop the same sparking sound with smoke while I tested at the same wall socket at my residence ! The reply to my query from the reapirer was that your earthing was not ok. I found my earthing very much ok. Then I suspected his earthing and I did the same thing means removed my earthing and it worked nicely though that's risky.

So, I understand that some insulation inside the UPS deteriorated due to that high voltage problem which rendered power failure in our locality and unless there is good earthing the leakage current will not flow and so no more sparking ! Is my understanding ok ? And if ok, plz guide me what further I should do to rectfy the problem as I don't have knowledge about UPS circuitry.

Thanks,

G. Medhi, Shillong

Register to Reply
Pathfinder Tags: earthing UPS circuit
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Sep 2007
Location: Wrong end of the yellow brick road in Oz
Posts: 930
Good Answers: 15
#1

Re: PC Problems: Smoking UPS

09/17/2009 11:27 PM

Question, how do you know your earthing is ok? you have very much resistance when testing with a ohm meter, how about with a Megger? doy ou get the same lower resistances? if you increase the current in the Earth, does the resistance increase (hot spots generated at the connection point between conductors)

Are you running any suppression equipment before the UPS?

__________________
Qn, Whats the differance between a Snake and a Onion? Ans, No one cries when you chop up a Snake
Register to Reply Score 1 for Off Topic
Member

Join Date: Sep 2009
Location: India
Posts: 8
#2

Re: PC Problems: Smoking UPS

09/18/2009 7:51 AM

Hi,

It seems the UPS T/Fs primary winding weakens due to overvoltage. When you removed earthing from UPS , now there is no leakage current from T/F to earthing terminal.It is risky to run UPS in present condition as your T/F is faulty . Try with interchaging the Phase & neutral at incoming side of UPS ,reconnect earthing to UPS.If the condition is same or got worse, replace T/F of UPS.

Register to Reply
Guru

Join Date: Sep 2009
Posts: 1056
Good Answers: 88
#3

Re: PC Problems: Smoking UPS

09/18/2009 2:32 PM

The first thing to go smoking in e.g a thunder caused power failure is the small metal varistor(s) located near your input voltage connector that is supposed to leak overvoltage surges to earth. If it's overstressed (too hi amps for too long) it can deteriorate in random (both ways up or down) change in voltage level of activation, in your case probably down.Check if tis is the case by temporarily disconnecting it but DONT under any surcomstances work with a no-ground powered computer

__________________
Life is complex. It has a real part and an imaginary part.
Register to Reply
Guru

Join Date: Sep 2007
Location: Wrong end of the yellow brick road in Oz
Posts: 930
Good Answers: 15
#5
In reply to #3

Re: PC Problems: Smoking UPS

09/19/2009 10:59 PM

I have found in the last that those devices don't just fail and come back to life, they either blow their sides off with a small hole thru the disc, or vanish from the PCB with only the stumpy legs left on the PCB

__________________
Qn, Whats the differance between a Snake and a Onion? Ans, No one cries when you chop up a Snake
Register to Reply Score 1 for Off Topic
Active Contributor

Join Date: Sep 2009
Location: Eugene Oregon
Posts: 16
#4

Re: PC Problems: Smoking UPS

09/18/2009 4:22 PM

Your Uninterrupted Power Supply (UPS) has a fused link to ground that needs to be replaced this is internal and in addition to it obvious circuit breaker which is on it's positive side. check both supplies and verify that these ground links are intact IE... if one is faulted it will act as if the ground " load / Nuetral" leads are reversed and cause the symptoms you have experienced when both PC's are plugged in.

__________________
People call me "Queue" for good reasons
Register to Reply
Guru
Hobbies - Musician - Tube Amps Only Please!

Join Date: Apr 2009
Location: Los Angeles, California USA
Posts: 553
Good Answers: 1
#6

Re: PC Problems: Smoking UPS

10/26/2009 11:49 PM

Just replace it. UPS devices only last about 5 years due to the lead-acid battery failure.

__________________
Regards, Maveric Manic - 'Knowledge is Power and Wisdom is knowing how to use it'
Register to Reply
Guru

Join Date: Sep 2007
Location: Wrong end of the yellow brick road in Oz
Posts: 930
Good Answers: 15
#7
In reply to #6

Re: PC Problems: Smoking UPS

11/10/2009 12:28 AM

Some UPS's have the batter "Pack" as a separate box.

The UPS I setup once used 96 x 2V cells wired in parallel/series configuration for 48 VDC terminal voltage, the cells were 3600Ah.

The battery "Pack" took up about 6 square meters of floor space and stood about 1200mm in height, including the cage they needed

__________________
Qn, Whats the differance between a Snake and a Onion? Ans, No one cries when you chop up a Snake
Register to Reply
Member
Engineering Fields - Power Engineering - New Member

Join Date: Aug 2008
Location: Surat Gujarat India
Posts: 8
#8

Re: PC Problems: Smoking UPS

12/15/2009 8:53 AM

Dear friends

Please see following links to understand What is earthing in electrical system

http://picearthingtech.com/

http://blogs.siliconindia.com/picearthingtech

Regards

Raju

__________________
Earthing is important but neglected
Register to Reply
Register to Reply 8 comments
Copy to Clipboard

Users who posted comments:

deept (1); maveric_manic (1); Queue (1); SimpleMind (1); Snaketails (3); Tamakuwala (1)

Previous in Forum: Leakage Currents   Next in Forum: Measuring Power Losses

Advertisement