Hopper Level Control

09/17/2009 7:01 AM

Hi,

I am having some trouble with a hopper on my plant. I need to be able to detect the level of material in the hopper to close a control loop on a vibro feeder. My problems are many. first, I can only use a non contact type of material sensor due to the temp and corrosive properties of the material. secondly the material is very abrasive. The hopper is also quite remote from any control equipment and cost dictates I use existing cables.

I am considering a two wire, loop powered, radar but have realised that my tec department are having trouble supplying an analog input card on the closest remote PLC rack.

My question is......is there a product that will allow me to power the "loop powered" radar and at the same time convert the 4-20ma return signal to a simple, (hopefully adjustable) digital output.

Any help???

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
2
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#1

Re: Hopper Level Control

09/17/2009 10:46 AM

You didn't give us enough information for a concise answer but you did give us enough for a sound start. As you stated your problem is in detecting the level in your hopper without touching it and you require this analog level to be a 4-20mA sensor. Without knowing the size of the hopper and what goes into the hopper, any answers from us will be just a guess. Radar though I'm certain is not what you want for this will likely not be cost effective. You might consider an ultrasound sensor pointed on an angle into the hopper. Another possible approach will be to include a load cell and to weigh the amount of additional material in the hopper. In any approach, I would let the decision making capability of your PLC to convert the analog signal (amount of material) to the digital add more material signal. In your PLC's software you should also be able to add some signal conditioning characteristics (hysteresis, timers) to prevent false triggers.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply Good Answer (Score 2)
Guru

Join Date: Apr 2007
Posts: 577
Good Answers: 10
#2

Re: Hopper Level Control

09/17/2009 9:07 PM

Can you please let us know what type is your material that you store in your hopper since your said, it is corrosive properties and the material is very abrasive?.

Secondly, what is your temperature of your material?.

__________________
Management is just like a bunch of Monkey sitting on a tall tree. Some climb to the highest branch and some at the lowest branch. The highest Monkey look down and see a lot of happy faces but the lower Monkey looks up and see nothing but all the....
Register to Reply
Member

Join Date: Aug 2009
Location: Memphis, Tennessee USA
Posts: 5
#3

Re: Hopper Level Control

09/18/2009 12:04 AM

Without seeing your operation, I would suggest you contact Globalspec or Thomasnet to find the closest product to fit your needs. Good luck.

__________________
John
Register to Reply
Guru

Join Date: May 2007
Location: Geelong, Australia
Posts: 1084
Good Answers: 54
#4

Re: Hopper Level Control

09/18/2009 12:07 AM

I've used a lot of radar, ultrasonics, lasers etc. and find it's often cheaper and more reliable to stick load cells under the hopper and weigh the material.

Then the type of material, dust, vibration, water content, angle of repose etc don't matter.

__________________
If there's something you don't understand...Then a wizard did it. As heard on "The Simpsons".
Register to Reply Score 1 for Good Answer
Power-User

Join Date: Jul 2009
Location: Montreal, Canada
Posts: 284
Good Answers: 18
#5

Re: Hopper Level Control

09/18/2009 12:23 AM

Assuming that you're looking to measure a continuous level ('continuous' is bad grammar ... continual in time, continuous in space), 4-20 mA-style, consider using an monitor/display, such as ones made by Moore Industries (http://www.miinet.com/products/sg_process.shtml). Install the monitor in your control room, run a signal cable to your measurement instrument, and presto!

If you need level alarming, make sure that the monitoring you choose have alarm switches built in.

Hope this helps!
DZ

__________________
Do unto others. Then run.
Register to Reply
Guru

Join Date: Jun 2009
Location: Bangalore, India
Posts: 725
Good Answers: 24
#6

Re: Hopper Level Control

09/18/2009 2:26 AM

http://www.sapconinstruments.com/admittance/sla.html

__________________
bioramani
Register to Reply
Anonymous Poster
#7

Re: Hopper Level Control

09/18/2009 12:10 PM

I like the load cell idea but theres one better , straine gauge on the legs or the cone it's self seen it liked it got it!

Register to Reply
Register to Reply 7 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); bioramani (1); DreadZontar (1); ffej (1); jcarter817 (1); redfred (1); Simon Wan (1)

Previous in Forum: VFD Power Savings   Next in Forum: MCCB Settings

Advertisement