My customer has started constructing a building without properly checking the the hydro in the area. Subsequently the utility only has single phase 14.4KV and the customer' requires 325KW of power, I know single phase what a nightmare!!!
I'm the electrical contractor and I'm proposing that we install 3 X 167 KVA transformers in parallel. This is only due to availability and cost not to have a 500 KVA single phase transformer.
As part of the fuse coordination study for the utility, the electrical engineer is unsure if the fault current of three transformers would be cumulative at the secondary connection point or would we use the average of the calculation of the three 167 transformers?
We have considered both sides but are still looking for a definitive answer and its reasoning.