LV cable size

12/24/2006 7:45 AM

hi,

dear all we are going to develop a set up for a gas field there we hav to develop the setp up desigined on 400v but the residential are is 300mtrs far away the designer suggested to use the step up transformer and i want to use the big size cable wht do u all say comment plz which is the better way?

regards

irfan choudhary

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Anonymous Poster
#1

Re: LV cable size

12/25/2006 1:55 PM

300m is not so long to justify step-up and step-down xfr 400/1000V. Use copper and make sure that the load is balanced otherwise, you will require a huge neutral return to carry out of balance current.

Reply
Participant

Join Date: Dec 2006
Location: PAKISTAN
Posts: 2
#2
In reply to #1

Re: LV cable size

12/25/2006 2:03 PM

thank you for your comments,the load is resdential and easily mangeable,but the genration voltage as i have told earlier that are 400 would u or any body else sugges the proper size eastiated

thanx

Reply
Anonymous Poster
#3

Re: LV cable size

12/25/2006 3:39 PM

Dear Irfan Choudhary,

In order to help with cable size, we would need some 'load` information.

I suggest you 'run the numbers` for the expected load.

You will require a step-down transformer for the residential load in any case.

A step-up transformer for transmission for the 300 M. run could eliminate
the transmission neutral and save a lot of copper balanced against the cost of
the step-up transformer and the increased cost of the higher primary step
down at the residence.

(This assumes you face statutory limits on voltage drop that cannot be
overcome by taping-up at the residence.)

Reply
Power-User
Popular Science - Weaponology - New Member Popular Science - Cosmology - New Member

Join Date: Apr 2006
Posts: 261
#4

Re: LV cable size

12/25/2006 3:41 PM

If you want sizes it might be a good idea to tell us

the size of the load.

Reply
Guru
Australia - Member - New Member Engineering Fields - Mechanical Engineering - New Member

Join Date: Sep 2006
Location: NSW Australia
Posts: 1101
Good Answers: 23
#5

Re: LV cable size

12/25/2006 5:17 PM

A coherent Question will elicit the correct answer

__________________
Dont get on to the roundabout if you dont know how to get off
Reply
Participant

Join Date: Dec 2006
Location: Petaling Jaya, Malaysia
Posts: 3
#6

Re: LV cable size

12/25/2006 10:33 PM

i think the usual copper cable would be enough..but don't make it too big..it's definitely not suits (if it's too big)..

__________________
A Friend In Need, Is A Friend Indeed
Reply
Anonymous Poster
#7

Re: LV cable size

12/26/2006 4:46 PM

My friend, it depends on your power consupmtion ( load.) Just a examle if your load is

400 Vac. 200 Amps. it means approx. 120 kVA. you should use for each phase 120 sqmm2 cupper cable. Mybe your load is 10 kVA. cable size will be less. but the most important thing is voltage dropping. Each 200 mt. your voltage average 8 volts drops. I think you don't need any step up transformer. You can solve your problem with the cable size... good luck with techinal researchs.. :)

Reply
Participant

Join Date: Dec 2006
Location: PAKISTAN
Posts: 2
#8
In reply to #7

Re: LV cable size

12/26/2006 11:32 PM

thank you respected friend,

further to my quiry my load ia 200kw(residential) approx.365Amps so accordoing to my calculation the voltage drop calculations we must be in need of 300 sq.mm cable for 300mtrs,

Maximum length of LV cable = L = 300 m,

Generated Voltage = V = 400 V

Current per phase = I = 360 Amperes

Assume Cable size of 400 sq. mm.

mV drop per Amp per meter = 0.17

Voltage drop = mV X I X L / 1000

= 0.17 X 360 X 300 / 1000 = 18.36 V

% drop = 18.36 / 400 X 100 = 4.59 % which is acceptable for lighting & domestic loads but not for Electrical motors

Reply
Active Contributor

Join Date: Jun 2008
Posts: 11
#9

Re: LV cable size

06/15/2008 3:50 AM

hi,

can you say the load approximately

__________________
Thanks and Regards,Krishnapillai.
Reply
Commentator

Join Date: Aug 2009
Posts: 91
#10

Re: LV cable size

10/28/2009 7:19 AM

Hello

Irfan ou need to keep the voltage drop < 3% ..

__________________
Correct me if i am wrong i am learner
Reply
Reply to Forum Thread 10 comments
Copy to Clipboard

Users who posted comments:

Anonymous Poster (3); garth (1); iffee5599 (2); ikhanuk (1); keerthi (1); Pragmatist (1); sh1f79ear (1)

Previous in Forum: Run 3 ph motor on singlephase   Next in Forum: Memory in PLC
You might be interested in: Cable Laying Services, Cable Assemblies, Cable Trays

Advertisement