Electrical Manhole Splices

09/28/2009 11:18 AM

A manhole electrical contractor plans on doing electrical manhole splices for 4160 volts.
What are electrical code requirements and things he should comply with?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#1

Re: Electrical Manhole Splice

09/28/2009 11:34 AM

He should look to the regulations appropriate for his locale.

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#2

Re: Electrical Manhole Splice

09/28/2009 11:41 AM

Consult your local codes. While they all are similar, you must meet the codes for your location. The local inspectors or local licensed electricians will know which codes you should follow. We cannot help you without knowing where the manhole bunkers reside. The electric codes in San Francisco CA, Denver CO, Fairbanks AK, Mumbai India, Sidney Australia and McMurdo Station Antarctica are slightly different for a reason.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Commentator

Join Date: Sep 2009
Posts: 59
#3

Re: Electrical Manhole Splice

09/28/2009 12:11 PM

I do not have a local code book handy.

I do know they electrical contractor has to submit his pull calculation and certifications. I am looking for what special tools are required, and how splices should be terminated. A picture would be helpful. I know once wire pull is done they have to Hot-Pot test the cables.

Is there anything else I am missing?

Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#4
In reply to #3

Re: Electrical Manhole Splice

09/28/2009 12:43 PM

I repeat myself when I'm in distress.

I repeat myself when I'm in distress.

I repeat myself when I'm in distress.

We cannot help you without knowing where the manhole bunkers reside.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#5
In reply to #3

Re: Electrical Manhole Splice

09/28/2009 8:08 PM

"I do not have a local code book handy."

"Is there anything else I am missing?"

What is missing is your ethical obligation to be cognizant of the local codes under which you are supposed to perform the job-at-hand.

You might get someone killed by following "on-line" code book interpretation.

Register to Reply
Power-User
Engineering Fields - Electrical Engineering - Hentoyk Philippines - Member - BRUTUS Saudi Arabia - Member - Brutus United Arab Emirates - Member - Brutus

Join Date: Aug 2009
Location: Gulf Region, IIEE_CRCSA
Posts: 113
Good Answers: 2
#6

Re: Electrical Manhole Splices

09/29/2009 6:49 AM

See NEC Article 300-5(e) though this povision applies better check with applicable local codes in your area or locality.

__________________
If there is a will... there is a way... No pain / No gain.
Register to Reply
Commentator

Join Date: Sep 2009
Posts: 59
#7
In reply to #6

Re: Electrical Manhole Splices

09/29/2009 11:46 AM

The city the manhole resides in is Bakersfield Ca.

Register to Reply
2
Commentator

Join Date: Nov 2007
Location: Third Rock from the Sun (?)
Posts: 76
Good Answers: 8
#8

Re: Electrical Manhole Splices

09/29/2009 3:00 PM

I've noticed a couple of things about your replys that lead me to believe that you are being less than honest with us. Based on your answers my guess is that you are either the contractor or the person that is supposed to be the inspector. In either case you don't know what you are doing. If you are the contractor you're going to get someone hurt by trying to BS your way through the job. If you are supposed to be the inspector make sure you get a nice steak and a few drinks from the contractor as he is going to do well on this job.

Your questions, "What are electrical code requirements and things he should comply with?" And your statement, "I do know they electrical contractor has to submit his pull calculation and certifications. I am looking for what special tools are required, and how splices should be terminated. A picture would be helpful. I know once wire pull is done they have to Hot-Pot test the cables. Is there anything else I am missing?" Are all answered nicely by LynLynch, "What is missing is your ethical obligation to be cognizant of the local codes under which you are supposed to perform the job-at-hand."

If you are in Bakersfield and if you are looking in a manhole that is not inside the fence of some sort of private enterprise you are probably looking at the property of Southern California Edison or whomever now owns them. That means two things. One is that they are a regulated utility company and are not governed by the National Electrical Code for residential wiring that everyone on this site is referring to. They, as are all public utilities, governed by an Electrical code that is about 75% thinner than the code book here on my desk. Second - - they have a construction standards book that provides detailed instructions on making 4160 splices. If you are a bonafide contractor, which I seriously doubt based on your statements here, you will have access to that information. If you use some good IBEW journeymen you may even get the job done right.

__________________
vagabond
Register to Reply Good Answer (Score 2)
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#9
In reply to #8

Re: Electrical Manhole Splices

09/29/2009 3:28 PM

You may not be perfectly accurate but you are quite right that something seems odd in the OP responses. You get a GA from me for your olfactory acuity.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Commentator

Join Date: Sep 2009
Posts: 59
#11
In reply to #9

Re: Electrical Manhole Splices

09/29/2009 5:42 PM

I am a SCADA/Instrumentation inspector helping with electrical inspections. I never intended to be dishonest. The electrical contractor for this new water treatment plant has been known to take short cuts.

I apologize to all for not recognizing the local code. I am not an electrican by trade, but a electrical engineer on the process and control side. My intent was to research how to do the job right. Please forgive me of my ignorance.

Again I never intended to be dishonet, but intended to find out how to do it right. Thanks to all for their input. Greatly appreciated.

Regards and God bless,

Rabat

Register to Reply
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#12
In reply to #11

Re: Electrical Manhole Splices

09/29/2009 5:59 PM

Ok, rabat, that seems cool - but next time, please just 'fess up & ask the question (with as much background as possible) directly - save a lot of bother & possible bad feelings all round.

John.

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply
Commentator
Canada - Member - New Member Engineering Fields - Mechanical Engineering - New Member Engineering Fields - Piping Design Engineering - New Member Hobbies - DIY Welding - New Member

Join Date: Aug 2008
Location: St. Albert, Alberta, Canada
Posts: 65
Good Answers: 11
#10
In reply to #8

Re: Electrical Manhole Splices

09/29/2009 3:50 PM

A quick review of Rabat's post entries shows he is repeatedly asking basic questions from the point of view of a consulting engineer or technician who is way out of his depth.

Rabat - Taking fees to undertake work to inspect and design items to which you are clearly incompotent to perform is unethical and a PUBLIC DANGER. Please stop the charade you are playing on this and the other posts you have written.

__________________
"You are, what you do, when it counts" - John Steakley (Armor) 1984
Register to Reply
Commentator

Join Date: Sep 2009
Posts: 59
#13
In reply to #10

Re: Electrical Manhole Splices

09/29/2009 6:33 PM

I just told the world that I am a SCADA/Instrumentation/DCS inspector helping with electrical inspection. I am not a consulting engineer or technician. You judge a book by it's cover.

The other post I have posted are for my general knowledge "Pumps, Space Heaters, grounding, etc". Again I am a SCADA/Instrumentation/DCS inspector.

I hear of alot of construction issues in the office and for answers I can't really find I'll post for my general knowledge or read other peoples post.

Please read and think before you post. Get to know someone before you judge them, rather than just crucify them for lack of information you have seen. I have been honest and direct ever since I have opened this account.

Rabat

Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#14
In reply to #13

Re: Electrical Manhole Splices

09/29/2009 7:06 PM

Why is," a SCADA/Instrumentation inspector helping with electrical inspections"?

You obviously are not qualified(no offense intended) to sign off on any work that you inspect. Since you would not necessarily recognize electrical problems like a qualified electrical inspector I wonder why you would incur such a potentially staggering lawsuit if your work kills someone. Oops, now I'm repeating myself.

The only crucifixion here was self inflicted!

Register to Reply
Commentator

Join Date: Sep 2009
Posts: 59
#15
In reply to #14

.

09/29/2009 7:55 PM

.

Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#16
In reply to #13

Re: Electrical Manhole Splices

09/29/2009 8:44 PM

Ok rabat, you've come clean with us now and everything does seem perfectly innocent. But, questioning somebody else's work skills by asking a group of anonymous people regardless of any individual credentials to verify or refute your concerns is circumspect at best. Now as I mentioned earlier, what you need to know are the pertinent codes from an authorized source. Anything less than that, regardless of the accuracy of the information, will put you in a bad position. So be careful what you say and to whom you bring your concerns.

Now as somebody else mentioned, there are different standards for power grid (utility) cabling and power user (NEC NFPA70) cabling. At first blush the differences in these two standards will seem odd when very heavy gauge cables (user) get clamped onto light gauge (utility) wires to complete a circuit, or a host of other apparent contradictions. So the differences you see in that bunker maybe intentional and quite correct.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Active Contributor

Join Date: Aug 2009
Location: Maryland USA
Posts: 24
#17
In reply to #13

Re: Electrical Manhole Splices

09/29/2009 11:03 PM

Since you do not seem to have the expertise for this type of project, I suggest you hire a consulting engineer that does and learn from him/her for your next project.

Register to Reply
Anonymous Poster
#18

Re: Electrical Manhole Splices

10/16/2009 11:41 AM

what is an electrical manhole

Register to Reply Off Topic (Score 5)
Register to Reply 18 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); bobrog (1); hentoyk (1); JohnDG (2); lyn (2); rabat (5); redfred (4); Steamerst (1); vagabond (1)