Using a 300VA Hammond demonstration transformer 60Hz single phase set up as a step up 1:2 with 120V input.
The following measurements and calculations were made at full load
Vp = 117V Vs = 228V
Ip = 2569mA Is = 1250mA
Pp = 325W
Pp = 301VA Ps = 285VA
Eff.% = 94.8%
Pf = 1.081 (Vs/Vp)
How do I calculate the total losses of the transformer at rated load?
Re: Calculating total losses of transformer in a test situation
09/30/2009 10:18 PM
pf> 1? (1.081)
despite that if you know efficiency don't you know losses?
why do homework here?
10/01/2009 11:03 AM
Before you try to calculate the efficiency you need to learn how to calculate the PF.
Clue : Its not "Pf = 1.081 (Vs/Vp)"
10/01/2009 5:39 PM
Why do homework here? ...... because I am a full time electrical engineering student as well as a single mom. Time is just not available to seek assistance at the college and this site was among my search results for answers.
Do you not wish to bolster students in your field?
10/01/2009 11:27 AM
10/01/2009 5:46 PM
According to my instructor Pf = W/VpIp so in this case Pf = 325W/117V x 2569mA. This is how I arrived at 1.081.
If you have any further information I would be glad to have your input.
10/01/2009 9:03 PM
Quote "Vp = 117V Vs = 228V Ip = 2569mA Is = 1250mA Pp = 325W
Pp = 301VA Ps = 285VA Eff.% = 94.8% Pf = 1.081 (Vs/Vp)"
VAp = Vp x Ip = 117 v x 2.57 amps = 300.7 VA not watts
VAs = Vs x Is = 228 v x 1.25 amps = 285 VA not watts
PF = watts/ VA
You do not have the value of watts. PF does not exceed the value of 1.0.
Watts maybe = to VA if PF = 1 but never greater than VA.
Drop the mA notation when you have these large values.
Good Answers: 88
10/02/2009 2:18 PM
Pin *(100-Eff%) or Pout*((100/Eff%)-1)
Pin=Vin*Iin*Pfin Pout=Vout*Iout*Pfout