earthing

10/03/2009 3:24 PM

In a PE/N supply will I have a large difference or by connecting two different groups of earth pits together while the distance between the two is about 60meters apart from each other ?

I am having analog signal problems

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Anonymous Poster
#1

Re: earthing

10/04/2009 7:56 AM

I started to address the problem but I realized that I do not understand PE/N supply.

Register to Reply
Guru
Canada - Member - Specialized in power electronics

Join Date: Feb 2008
Location: Montreal, Canada.
Posts: 1372
Good Answers: 80
#2

Re: earthing

10/04/2009 9:12 AM

You didn't provide enough details for us to help you.

Do a search on this site and you will find many discussions regarding grounding issues and analog signal shielding problems.

Good luck.

__________________
Experienced is earned, common sense is taught, both are rare essentials of life.
Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#3

Re: earthing

10/04/2009 9:38 PM

Possibly (but it depends on the sort of analog equipment, isolation devices and interconnection and interaction between them).

A good (compliant to local regulations) safety earth does not necessarily mean a good analog signal earth. If you are having issues with signal noise (which you mention you are having) then consider connecting your signal earths to a single (star) point to minimise earth loops, or possibly a separate isolated analog earth connected to the main safety earth at a single point.

Hopefully this general information helps. Also see the numerous previous threads on CR4 on earthing and grounding for more information.

Can you provide more detailed information on your site, its wiring setup and its problems?

__________________
jack of all trades
Register to Reply
Register to Reply 3 comments
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); jack of all trades (1); marcot (1)

Previous in Forum: Shock   Next in Forum: Intersecting of 2 cirlces of equal diameter
You might be interested in: Signal Conditioner Chips

Advertisement