Hello everybody
Is there a formula relating area of core to maximun power transfer of an iron cored tranformer with E I laminations of silcon steel
230 v 50 Hz supply in my country
I have some old transformers I wish to rewind
Thank you
Re: Maximum Power Transfer Formula
10/06/2009 5:00 PM
10/07/2009 12:10 AM
Rulrs of thumb for one off second hand transformer winding.
1) Milk the previous design, if still working the primary can be salvaged, low voltage secondries turns noted and turns per volt calculated. If the ratings are known the total VA can be noted.
2) If burnt out and specification known primary turns can be counted; & VA from 3) if uncertain.
3) For a bare core the rules are:- Is it scrapless laminations? Take two E shaped laminations, put them leg to leg, the I lams should have come from the winding spaces. They are commonest so here is your answer:-leg area =stack height X tongue. At 50Hz 50 X A squared = watts; 8 sq ins per volt(divide 8 sq" by leg area).
4)Make primary build 35% of window height and secondary loss (in wire heating) similar to primary.