Participant

Join Date: Oct 2009
Posts: 1

ELCB CONNECTION

10/10/2009 4:09 AM

We are having 440V 32Amps ,3 Phase Welding machine , which is having R Y B phase supply plus Earth connections. We want to connect a 4 Pole ELCB for earth fault protection. What is the connection we need to give in that 4 poles...(Whether RYB+E or RYB+N)....? If it is neutral means how to give that connection.....?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User
New Zealand - Member - Kiwi

Join Date: Oct 2007
Location: Christchurch, New Zealand
Posts: 328
Good Answers: 29
#1

Re: ELCB CONNECTION

10/10/2009 4:47 AM

The ELCB will work correctly if you just connect the 3 phases through it, and leave 1 pole spare.

If you want the test button to work, usually the pole left unconnected should be one of the outside poles, 1 or 4, as the test button works between poles 2 and 3.

__________________
paulusgnome
Register to Reply
Anonymous Poster
#3
In reply to #1

Re: ELCB CONNECTION

10/10/2009 10:04 AM

It was a new knowledge for me that the ELCB works in 3 phase with no neutral.!!!Will it work actually ?Have u ever seen this......?

Register to Reply
Power-User
New Zealand - Member - Kiwi

Join Date: Oct 2007
Location: Christchurch, New Zealand
Posts: 328
Good Answers: 29
#4
In reply to #3

Re: ELCB CONNECTION

10/10/2009 3:02 PM

Seen, it, done it many times, mainly when protecting reefers (refrigerated shipping containers) which all have 3-phase motors (no neutral) and must be RCD-protected in container parks here (NZ).

A basic grasp of 3-phase theory will greatly assist you in understanding how this works.

__________________
paulusgnome
Register to Reply
Anonymous Poster
#6
In reply to #4

Re: ELCB CONNECTION

10/11/2009 5:11 AM

I have a thourough idea of the working of ELCb,where it continously samples the phase n neutral sum of which will be zero always......Ia+Ib+Ic+In=0...in 3 phase systems Ia
+Ib+Ic=0...but I haven't seen a 4p Elcb working on a 3 phase systems........

Register to Reply
Anonymous Poster
#7
In reply to #6

Re: ELCB CONNECTION

10/12/2009 5:05 AM

As yours is a 3-phase balanced kind of load, here there will not be any neutral current. All the three phases will be loaded equally. Still your equation will hold good.

Ia + Ib + Ic + In = 0

(i.e.) Ia + Ib + Ic + 0 = 0 in your case.

Any earth fault inside the machine, this balance is affected and the ELCB operates.

Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#2

Re: ELCB CONNECTION

10/10/2009 7:42 AM

I agree with Paul, but ensure the working of the TEST facility after connecting as above.

Register to Reply
Anonymous Poster
#9
In reply to #2

Re: ELCB CONNECTION

10/16/2009 1:13 PM

Its never possible as Ia+Ib+Ic =0 in 3 wire system and if u connect 4p ELCB in that system the total current of that is always zero.So no net induction to the coil on earth fault is also zero.........

Register to Reply
Anonymous Poster
#5

Re: ELCB CONNECTION

10/11/2009 1:50 AM

RYB+N should be coonected to ELCB AND EARTH IS CONNECTED ALSO BUT DIRECT TO EARTH BAR

Register to Reply
Anonymous Poster
#8
In reply to #5

Re: ELCB CONNECTION

10/12/2009 11:46 AM

Thanks to all friends.. But only thing is if i connect only RYB means it is necessary to connect the earth also with that..?

Register to Reply Off Topic (Score 5)