What is the procedure for using a Meggar for measuring IR value of cable, motors etc?
"Knowledge and human power are synonymous." -- Francis Bacon
Re: meggar using procedure
10/21/2009 1:58 PM
I'd use the procedure specified in the operator's manual.
Really, you do have the manual, don't you?
Maybe you could search for the model # of your particular machine if you don't.
10/21/2009 2:57 PM
I do not disconnect the wires of the supply cable in the motor's contact box if, for instance, I have to make a "high pot" test (against earth) of an induction motor which has only one set of windings and there are only 3 leads. If I measured "near to infinity" resisatance I am satisfied and if the mechanic I am with disapproves my procedure saying "According to rules, you need to disconnect the supply leads in the box", I leave him the pleasure of turning the nuts, upon what, having repeated the test, I report to him, now satisfied too, again "near to infinity."
But, caution: only if contactor(s) are used, not a soft starter (the more so a VFD) !
11/02/2009 3:40 PM
But you sure do disconnect the supply, don't you??
Re: Meggars and Measurements
10/22/2009 12:53 AM
thank you all, but it would be nicer if u be more precise would'nt it.