SHUTDOWN VALVES

10/22/2009 2:45 AM

Does shutdown valves have positioners ?

Also the role, importance and functionality of solenoid in operation of a shutdown valve?

Register to Reply
Pathfinder Tags: Shutdown valves
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User

Join Date: Mar 2008
Location: Mumbai
Posts: 250
Good Answers: 2
#1

Re: SHUTDOWN VALVES

10/22/2009 4:02 AM

Yes For PST , But only if Client Requires so

Regards

Jose

Register to Reply
Anonymous Poster
#2
In reply to #1

Re: SHUTDOWN VALVES

10/24/2009 11:48 AM

shut down valave doesnt require positioner as noboady controls it . Limit switch gives the information whether the valve is open or close. Main purpose of shutdown valve is incase of air fail the valve closed promtly or operator can close it through soleniod.

Sudip

Register to Reply
Power-User

Join Date: Mar 2008
Location: Mumbai
Posts: 250
Good Answers: 2
#3
In reply to #2

Re: SHUTDOWN VALVES

10/24/2009 4:07 PM

Grow Uppp

Positioners are used in Shutdown Valve for Partial Stroke Testing

Shutdown Valves rarely operate during normal ops, Chances are that valve may get struck when it is required for shutdown

So operators use PST technique to check the Performance of Shutdown Valve

This is the trend in O&G sector

Regards

Jose

Register to Reply
Commentator
India - Member - Naveen Menon Engineering Fields - Instrumentation Engineering - Naveen Menon

Join Date: Oct 2007
Location: India
Posts: 92
Good Answers: 2
#4

Re: SHUTDOWN VALVES

11/05/2009 4:30 AM

you may require to operate sd valve at some percentage opening at a partila failure of a loop to prevent some downstream equipment , like open the sd valve 50% one shot if a particular compressor surges etc. Then you require positioner,

If you do not need control of the sd valve at any stage and its only for the full open close methodology then the positioner might not be required since it will only add another instrument to the loop that may fail, so one needs to make a descision based on the requirement of the process, Always better to keep number of components in aloop to the minimum to increase reliabilty, reduce downtime and also troubleshooting time.

Regards

Prince

Register to Reply
Register to Reply 4 comments
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); josej (2); naveen_menon (1)

Previous in Forum: Actuators and Positioner   Next in Forum: Types of Pigtail Siphons (Other Than Straight and L)
You might be interested in: Solenoid Valves, Pressure Relief Valves, Gas Valves

Advertisement