Pad Mounted Transformer

10/26/2009 3:27 PM

Needing a little help I have a 480v 3 wire delta padmount transformer wanting to float b phase. I talked to the transformer comany they said no problem. When I look in metering book it only shows grounded b phase 2 cts 5s meter. What will happen if I dont ground b phase? Any help would be greatly appreciated. Chip

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User

Join Date: Jun 2009
Posts: 134
Good Answers: 11
#1

Re: Pad Mounted Transformer

10/27/2009 12:57 PM

What would happen if there was a short from primary to seconday.

These shorts do happen.

Register to Reply
Guru

Join Date: Jul 2008
Location: SoCal USA
Posts: 556
Good Answers: 23
#2

Re: Pad Mounted Transformer

10/27/2009 1:29 PM

Dear Wango,

The grounding is a safety issue, not a metering issue, unless of course the power provider has a requirement about grounding B phase.

As long as you use B phase as the ending potential, with CT's in A and C phases, your meter will have what it needs to register correctly.

I strongly recommend that you have alarms to reveal grounding of one of the phases so you can correct the condition before a second phase grounds, either that or a current limiting grounding system.

Regards, CJM