An industrial plant with district (internal) load of 60 MW and GE STG 2X11 MW (operated at 8 MW) and GE CGTGs 3X42 MW (operated on preselected load of 28 and droop mode of 5%)and is connected to the power grid. The typical generation is 100 MW total and the power export is 40 MW. When disconnected from the grid, the frequency increases to 61.5 Hz. One of the CGTGs mode was manually changed 65 seconds after disconnection to Isoch to control the frequency. Within 7 seconds The Isoch CGTG tripped on low forward power that is set to trip on 2% load and 3 seconds delay (Mark V alarmed with reverse power). The frequency then changed to 60.8 and the other two CGTGs still on droop started immediately increasing speed and reached 62.2 Hz. What is the reason for the unit on Isoch to trip? Why the droop units started increasing speed? Is there a solution? Is it ok to disable the low forward power trip point and rely on reverse power of the protection relay and the turbine..