Earthing Armored Cable

11/10/2009 12:31 PM

Is there any problem if we earth the armour of the cable at both ends?Should we take precaution in that case as not to earth the both armour of the cable ends.

__________________
"Know something about everything and everything about something"
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User

Join Date: Feb 2009
Location: CT USA
Posts: 257
Good Answers: 14
#1

Re: Earthing Armored Cable

11/10/2009 4:02 PM

Do a google search for the term "Ground Loop".

I am not an electrical engineer but,

I think you will find having more than one ground is usually a bad idea.

Register to Reply
Guru
Safety - ESD - New Member India - Member - New Member Engineering Fields - Energy Engineering - New Member

Join Date: May 2007
Location: Pune , India
Posts: 875
Good Answers: 42
#2

Re: Earthing Armored Cable

11/10/2009 7:34 PM

This subject was discussed earlier also in this forum( thread on on 07/24/2009)

http://cr4.globalspec.com/thread/40950/Armored-Cable-and-Earthing

Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#3

Re: Earthing Armored Cable

11/12/2009 9:14 AM

If it is a multi-core cable, then there is no issue in earthing the cable armour at both ends. But, if it is a single core cable, then earthing at only one end is mandated, as earthing at both ends, in such a case, would circulate eddy currents in the armour and heat it up.

Register to Reply
Register to Reply 3 comments
Copy to Clipboard

Users who posted comments:

Calnet42 (1); electricalexpert65 (1); V.I.Abraham (1)

Previous in Forum: Transformers: Restricted Earth Fault vs. Differential Protection   Next in Forum: Control and Protection Circuit for Palleling Transformers
You might be interested in: Cable Laying Services, Cable Assemblies, Cable Trays

Advertisement