Motor Control

11/11/2009 7:09 AM

Good morning I have a problem and would love help and advice.I put two motor 1/3 hp and control them with a Baldor driver.But when i push the start button I can hold one motor with my hand it didn't run, but I cant hold the other. Do I miss a parameters or the driver is being

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Engineering Fields - Electrical Engineering - Analog and Digital Circuit Design Engineering Fields - Electromechanical Engineering - Transformers, Motors & Drives, EM Launchers Engineering Fields - Engineering Physics - Applied Electrical, Optical, and Mechanical

Join Date: Jan 2008
Location: NY
Posts: 1207
Good Answers: 119
#1

Re: Motor Control

11/11/2009 9:13 AM

For AC motors/drives, there is a starting torque or current limit parameter. It can usually be set over 100% to get optimal starting performance. I believe one or more of the parameters is set differently between your 2 drives.

The AC drives I've used have over 60 programmable settings, several of which can affect the peak current/torque. I normally step through every parameter and write the values down for future reference. Verify that each drive has the same parameters and you should get identical motor performance.

DC drives have fewer parameters, but the same idea applies. Verify each drive has the same settings.

Register to Reply Score 1 for Good Answer
2
Power-User

Join Date: Jul 2008
Location: UK
Posts: 205
Good Answers: 50
#2

Re: Motor Control

11/12/2009 4:47 PM

If I understand you correctly, they are both connected to one VFD output but one motor is not developing much torque.

If this is the case, then the motor is likely connected for a higher voltage. reconnect it to the VFD output voltage level and it should be much better. Check the nameplate for correct connection for your voltage.

Your post is not too clear so I hope this is the correct interpretation and may help

__________________
Something new every day!
Register to Reply Good Answer (Score 2)
Anonymous Poster
#3
In reply to #2

Re: Motor Control

11/13/2009 6:07 AM

Thanks Malcom. I did look all that they both are the same motor what I did yesterday is I increase the torque and it seem working good.Thank you all for your shoot.

Register to Reply
Register to Reply 3 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); MalcolmK (1); mjb1962853 (1)

Previous in Forum: Energy meter   Next in Forum: Busbar Selection and Ampacity

Advertisement