IEEE Standards for Connecting Ground Grids

11/18/2009 10:50 PM

Hello , Im looking for info about ground gris, specifically when you could or could not connect them together ( two ground grids). I was looking some Ieee stdandars (ieee80-81) but I found only info about design, maybe I dont know how to search this Idea in inglish :P. I`d really appreciate if someone can help me and give me some Idea or where to find the answer. Thanks A student from South America,Chile.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Anonymous Poster
#1

Re: IEEE Standards for Connecting Ground Grids

11/20/2009 8:55 AM

According to NEC (NFPA-70, and NFPA-780) you SHOULD connect ALL the grounding grids in order to avoid induced dangerous potentials in separated grids.

The connection can be made between grounding rods from each grid.

Reply
Guru

Join Date: Aug 2007
Location: Indiana, USA
Posts: 579
Good Answers: 61
#2

Re: IEEE Standards for Connecting Ground Grids

11/20/2009 10:13 AM

The best IEEE reference for this is IEEE 142, Recommended Practice for Grounding of Industrial and Commercial Power Systems. It is also known as the "Green Book". If you are studying power engineering, I strongly recommend you get very familiar with all of the IEEE Color Books. They are a great resource for beginners and experienced professionals.

The specific question you ask may not be answered directly. When two ground grids are connected together, you essentially have one larger grid. You must then review the design of the entire grid system as a single unit. Some areas which must be analyzed:

  • Do the connections between the two grids have sufficient conductivity to allow fault current to flow to all grounding electrodes? Connecting the grids at one or two points may actually reduce the effectiveness of both grids.
  • Does one grid have a higher earth resistance than the other? If so, fault current will tend to flow to the electrodes with the lower earth resistance.
  • Are the grids of the same design (similar type & spacing of electrodes & conductors)?. Dissimilar materials may lead to galvanic corrosion of the grid, while unequal spacing may create localized differentials in earth resistance.

These are a few of the questions to resolve. If I were to analyze this, I would do a basic design for a single, large grid, then compare my design to the proposed combination of 2 existing grids. I would then perform in-depth analysis of any parts of the proposed grid combination which were different from my single-grid design, to ensure the proposed grid provided an adequate alternative.

__________________
Experience: The knowledge you gain just AFTER you needed it.
Reply
Anonymous Poster
#3
In reply to #2

Re: IEEE Standards for Connecting Ground Grids

11/20/2009 10:34 PM

Thank for the answers you really helped me.

Reply
Participant

Join Date: Sep 2015
Posts: 1
#6
In reply to #2

Re: IEEE Standards for Connecting Ground Grids

09/24/2015 3:58 PM

Hi...I have some inquiries that would fall under this discussion.

I understand the part of calculation what you describe and thanks very much for that. My concern would be after the calculation, if everything is ok, how do you perform the task? In other words, when it comes to connect a bare copper between two grids? It is impractical to de-energize the whole substation during this task, while performing the task when the substation is energized..we have to consdier the we are working with a live system..any fault that happen during that time would go through the workers and a serious safety concern..in addition..as during the work we have to dig..step and touch potential could be violated...

i just dont know what would be the mitigation or how we can proceed..of-course my back ground is not utility scale grounding but that's an area i am looking into right now...any advise would be highly appreciated..

Thanks

Arif

Reply
Member

Join Date: Nov 2009
Location: jakarta, indonesia
Posts: 6
#4

Re: IEEE Standards for Connecting Ground Grids

11/22/2009 9:50 AM

IEEE_Std_142-1991_Grounding_of_Industrial_and_Commercial_Power_Systems

you can get it from www.rapidlibrary.com. its free,

__________________
power plant electrical engineer
Reply
Anonymous Poster
#5
In reply to #4

Re: IEEE Standards for Connecting Ground Grids

11/30/2009 12:26 PM

It's also illegal.