This is a follow up thread to the one I posted last month. I performed the "experiment" of turning off all the loads in the building at the switchgear and taking note of the readings on the meter. The meter is on the primary side of the transformers. The arrangement they have with the meter is that only two legs of the 4800 volt delta circuit are recorded. At the point that no loads were on the transformers, the data read:
Phase A current=.046 A
Phase B current = 0 A
Phase C current = .081 A
Power Factor = .164
Phase A, B, C voltages were all 120-121 Volts
The meter multiplier is 3200. (40 for voltage and 80 for current)
So, I calculated the winding power as follows
(Ave current) * (square root of 3) * (3200) * (volts) * (PF)
(.0635) * (1.732) *(3200) * (120) * (.164) = 6926 watts or roughly 7 kw
I know how many hours on a monthly or annual basis the facility is running at "idle" so I can get to a kWh value and a dollar cost.
However, I still need to calculate the losses when the transformers are under load. The power factor of the facility is basically one of two values: .85 when the facility is operating and .58 when the facility is in idle mode.
Do I have enough information to estimate the losses of the transformers?
Thanks for any advice and assistance.
LTU student
Michigan, USA