Anonymous Poster

phase sequence

11/28/2009 5:23 AM

hi experts!!

i have 3 identical 1750kva 11kv alternator.one of this recently winding damaged and now rewinded line up done and checked alone voltage ok,but the phese sequence also checked its same as remaining.can i syncro with other? if the phese sequence correct or not how do i conform? boz mirror phase sequence also shows same indication isit?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User
Engineering Fields - Electrical Engineering - Hentoyk Philippines - Member - BRUTUS Saudi Arabia - Member - Brutus United Arab Emirates - Member - Brutus

Join Date: Aug 2009
Location: Gulf Region, IIEE_CRCSA
Posts: 113
Good Answers: 2
#1

Re: phase sequence

11/29/2009 1:44 AM

You can not hook the gen sets or multiple gen sets into parallel operation to be coupled in substation bus bars unless you meet the criteria.

1. Must be the same phase sequence.

2. Must be the same voltages.

3. Must be the same frequency.

__________________
If there is a will... there is a way... No pain / No gain.
Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#2

Re: phase sequence

11/29/2009 3:39 AM

Aren't you aware of the Dark Lamp method or the Bright Lamp method? If the phase sequence is different it would indicate in any of the above methods.

Reply
Active Contributor

Join Date: Nov 2008
Location: Bangalore
Posts: 22
#4
In reply to #2

Re: phase sequence

11/30/2009 12:21 AM

Kindly explain the Dark / Bright lamp methods to synch the generators. Good literature with dwg would help us better.

__________________
Let Noble Thoughts Comes to Us From All The Sides
Reply Off Topic (Score 5)
Power-User

Join Date: Oct 2009
Location: Istanbul. European side
Posts: 151
Good Answers: 4
#6
In reply to #2

Re: phase sequence

12/01/2009 7:39 AM

The most safe method is Dark lamp or Bright lamp method as mentioned by electricalexpert65.

Other PLC methods can be used for the perfect generators, of which in the factory performance and no doubt of their communication with each other. And therefore paralleling can be achieved automatically without any person to help.

If you are in doubt with your generators, you must first use the old and safe method to approve if they are O.K and suitable for automatically paralleling.

Reply
Anonymous Poster
#7
In reply to #2

Re: phase sequence

12/01/2009 10:22 AM

thxxxx..... kindly tell me the procedure??

Reply
Power-User

Join Date: Oct 2009
Location: Istanbul. European side
Posts: 151
Good Answers: 4
#8
In reply to #7

Re: phase sequence

12/02/2009 5:00 AM

This is the dark lamp connection. lamps are connected across the same phase side of the common busbar. (R to R, S to S and T to T

Lamps will be on an off successively and later When the both lamps go dark, it is considered that two side of each lamp group is in the same phase and same angle.

Then you can make both switches on, providing the lamps stay off at least 3 seconds.

In the event the generators, to be paralleled, are more than two, then it is a good way to synchronize each generator directly to the common busbar. In this case one sides of each lamp group must be connected to the busbar, and the other side to the generator to be synchronized.

Bright lamp connection is almost the same, except the lamps are connected on different phases.

Reply
Power-User
Engineering Fields - Electrical Engineering - Hentoyk Philippines - Member - BRUTUS Saudi Arabia - Member - Brutus United Arab Emirates - Member - Brutus

Join Date: Aug 2009
Location: Gulf Region, IIEE_CRCSA
Posts: 113
Good Answers: 2
#3

Re: phase sequence

11/29/2009 4:09 AM

Well it seems dark lamp method anold fashoin way i did it many times meaning having the lamps of equal wattage put on the same impressed voltage gives the same brightness. Nowadays we are using PLC then.

__________________
If there is a will... there is a way... No pain / No gain.
Reply
Active Contributor

Join Date: Nov 2009
Posts: 20
#5

Re: phase sequence

11/30/2009 4:32 AM

I can suggest more practical way,if you can isolate bus section and put only one generator on it and start any one motor if it rotate in same direction as with other generator phase sequence is OK