DISTANCE AND DIFFERENTIAL PROTECTION

11/28/2009 11:51 AM

Hi

I want to know what is the difference between DISTANCE PROTECTION & DIFFERENTIAL PROTECTION?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
2
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#1

Re: DISTANCE AND DIFFERENTIAL PROTECTION

11/29/2009 3:31 AM

Distance Protection is for Transmission Lines and works on the principle of calculating the impedance up to the point of fault. It needs both Voltage Input & Current Input.

Differential Protection operates on the principle of calculating the difference between two currents inputted to the relay. It is used for machines like Transformers, Generators, Motors and also for Bus bars in sub-stations. You need to give two current inputs to the relay.

Register to Reply Good Answer (Score 2)
Active Contributor

Join Date: Aug 2008
Posts: 11
#2
In reply to #1

Re: DISTANCE AND DIFFERENTIAL PROTECTION

12/03/2009 4:49 PM

I agree, you can also use differential protection to protect short overhead lines and it is usually the main type of cable feeder protection using relays such as solkor and translay in conjunction with pilot wires. The rule of the thumb in differential protection is 'what goes in must equal what comes out'

__________________
Opportunity is missed by most because it is dressed in overalls and looks like work
Register to Reply
Commentator

Join Date: Jan 2010
Posts: 73
Good Answers: 1
#3

Re: DISTANCE AND DIFFERENTIAL PROTECTION

01/03/2010 6:29 PM

spelling...joke.. the difference is that the way how these relays work or the principles they are using. 1st, the distance relay, it calculates the impedance of the protected equipment, if the calculate impedance is less than the impedance of the protected equipment (typically 80%) it will then issue a tripping signal - which means there is a fault. 2nd, Differential relays, are unit protection, it compared the in and out of certain quantities that flow across the protected equipment, most likely, it compares the in - out of currents. I hope it is clear.

Register to Reply
Register to Reply 3 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

electricalexpert65 (1); hkian (1); jmd (1)