how to calculate capacitor values

11/30/2009 9:05 AM

How to calculate the capacitor values of the power factor maintained

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Safety - ESD - New Member India - Member - New Member Engineering Fields - Energy Engineering - New Member

Join Date: May 2007
Location: Pune , India
Posts: 875
Good Answers: 42
#1

Re: how to calculate capacitor values

11/30/2009 9:28 AM

KVAR of the Capacitance needed to be added in the circuit = kW ( tanΦ1 -tan Φ2)

Cos Φ1 the present Power factor of the system

Cos Φ2 The Value of the required Power factor improvement

Reply
Active Contributor

Join Date: Mar 2008
Posts: 15
Good Answers: 3
#2

Re: how to calculate capacitor values

12/02/2009 8:53 AM

Calculation of Required Power Factor

The reactive power which is necessary to achieve a desired power factor is calculated by the following formula:

QC = P • F
QC - Reactive power of the required correcting capacitor
P - Active power of the load to be corrected
F - Conversion factor according to chart

Original Power
Factor

Conversion Factor for a Target Power Factor

COSf1

COSf 2

0.70

0.75

0.80

0.85

0.90

0.92

0.94

0.96

0.98

1.00

0.203.8794.0174.1494.2794.4154.4734.5364.6074.6964.899
0.252.8532.9913.1233.2533.3893.4473.5103.5813.6703.873
0.302.1602.2982.4302.5602.6952.7542.8172.8882.9773.180
0.351.6561.7951.9262.0572.1922.2502.3132.3852.4732.676
0.401.2711.4091.5411.6721.8071.8651.9282.0002.0882.291
0.450.9641.1031.2351.3651.5001.5591.6221.6931.7811.985
0.500.7120.850.9821.1121.2481.3061.3691.4401.5291.732
0.550.4980.6370.7680.8991.0341.0921.1561.2271.3151.518
0.600.3130.4510.5830.7140.8490.9070.971.0421.1301.333
0.650.1490.2870.4190.5490.6850.7430.8060.8770.9661.169
0.700.1380.270.40.5360.5940.6570.7290.8171.020
0.750.1320.2620.3980.4560.5190.590.6790.882
0.800.130.2660.3240.3870.4580.5470.75
0.850.1350.1940.2570.3280.4170.62
0.900.0580.1210.1930.2810.484
0.950.0370.1260.329

For Example

a.Consumption of active energy: ………EW = 300000kWh

b.Consumption of reactive energy: ………EB = 400000 kvarh
c.Number of working hours: …………t = 600 h

Resulting average active power:P = = 500kW

Calculation of the original power factor cosφ1:

cosφ

1=

For the improvement of the power factor from 0.6 to 0.9 we read the factor 0.849 from the chart above.

The required capacitor power is: QC = 500kW•0.849 = 425 kvar

To Calculate Capacitors capacitance, Formulae are as under:

Xc= 1/(2*3.142857*fC)

Xc=(Kv²)* 1000/Kvar

C=(Kvar*1000)/((2*3.142857*f)*(Kv²))

Kvar=1000*(Kv²)/Xc

Where

f = Frequency

C = Capacitance

Xc = Capacitive reactance

Kvar = Kilo Reactive Power

Kv = Kilo volts

Reply
Associate

Join Date: Nov 2009
Posts: 39
Good Answers: 4
#3

Re: how to calculate capacitor values

12/04/2009 2:48 AM

Its Very simple.

Required capacitance value is KVAr= KVA*SinPhi = KVA ( Sin ( Cos inv. ( Power facror) )

OK?

Reply
Active Contributor

Join Date: Mar 2008
Location: Switzerland
Posts: 17
#4

Re: how to calculate capacitor values

12/04/2009 9:56 AM

Another modified way of calculating the Capacitor rating

1. Capacitor Rating Required (KVAr) = KW x M.F.

2. M.F. = tan (phi -1) - tan(phi-2)

Where as cos(phi -1) is present p.f. & cos(phi-2) is desired p.f.