Residual Voltage Transformer (RVT)

12/04/2009 6:31 AM

How to find the residual voltage appeared across open delta winding of Residual Voltage Transformer connected to star connected 2300 kvar, 11 kv, per phase 8 units when one, two, three upto seven units fails.?

Register to Reply
Pathfinder Tags: residual voltage
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#1

Re: RVT

12/04/2009 8:45 AM

Very interesting question though!

I feel that the output voltage of a residual VT is not affected by the load connected to the primary bus. As long as there is no earth fault, RVT Secondary will not have any voltage. The theory is simple:

Supposing that you have a 110V rated RVT Secondary,

i) Ungrounded System or Grounded System - No ground fault - No secondary voltage across the Open Delta RVT Secondary

ii) Ungrounded System - Ground fault in one phase in the primary bus -RVT Secondary voltage will be 3 times the Phase Voltage of the RVT Secondary rated voltage

iii) Solidly Grounded System - Ground fault in one phase in the primary bus - RVT Secondary Voltage will be the phase voltage of the RVT Secondary rated voltage.

Register to Reply
Associate

Join Date: Feb 2009
Posts: 35
#2

Re: Residual Voltage Transformer (RVT)

12/28/2009 5:38 AM

Your question is not completely understood, have seven RVTs failed in service?

If the RVTs are failing it maybe that your earthing system & RVT loading & connection are the problem.

"Introduction to Instrument-Transformers" by Brian D Jenkins, George Newnes Ltd publication 1967, Chapter 21, the end of section on Types of VTs- Various Fault & other abnormal conditions may help in your predicament.

Also see CR4 discussion on "Tarriff Metering on Earthed Voltage Transformers-Fig2" for Inversion vector diagram & better understanding of what maybe taking place.