Overcurrent Relays

12/04/2009 8:10 AM

Dear Experts,

I have come across that in some practice, overcurrent relays are only installed for installation with loading current >300A and the overcurrent relay can be waive for installation <300A.

Can anybody tells me why?

p/s: Earth fault relays are use in all installation.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#1

Re: overcurrent relay

12/04/2009 8:31 AM

Earth faults can cause fatal harm to humans, even loss of life. Spend whatever you might, it is impossible to bring back a life lost.Isn't it? So, earth fault relays are mandated in all electrical installations.

Over current/Short circuit faults might cause harm to the property/installation, which might be resurrected by spending some money. The choice of having over current protection or not - hence - is decided by the person's willingness to take a risk to allow his installation/property to get damaged during a overcurrent fault.

There is no rule or limit to have or not to have overfcurrent protection below 300A feeders. I have come across overcurrent protection in feeders as low as 16A. So, there is no hard and fast rule on that.

Register to Reply Score 1 for Good Answer
Anonymous Poster
#2

Re: Overcurrent Relays

12/04/2009 12:01 PM

In our factory the over current protections are there for the lower currents too (ACB tripping mechanism)

The ACBs are on Lines are as high as 800A FLC to some of less than 100A FLC.

Register to Reply
Commentator

Join Date: Dec 2009
Location: Jakarta 12130 Indonesia
Posts: 76
Good Answers: 1
#3

Re: Overcurrent Relays

12/14/2009 1:35 AM

I have experienced, that contractor designed the MCC low voltage feeder which has 100A breakers and less are not provided with specific earth fault relay. System is implementing solid grounded.

The reason (contractor explained) is that the groundfault current is detected by breaker, therefore no need RCD. Are there any opinion?

__________________
RSM Elect Specialist
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#4
In reply to #3

Re: Overcurrent Relays

12/14/2009 8:19 AM

That depends upon the system of earthing. If it is TN (both TN-C & TN-S) - then you don't need any seperate RCD as any earth fault would be phase-neutral short and a very high current would flow such that any overcurrent protective device or short circuit protective device itself would identify and isolate the supply to the system.

If it is TT then you definitely need an RCD because the magnitude of the earth fault current now would be depending upon the earth resistance and would be in ohms. As such any over current protective device or short circuit protective device may not sense this fault and the system would continue to be faulty even causing a probable danger to human life and/or property. So, an RCD is mandatory in such systems.

Register to Reply Score 1 for Good Answer
Register to Reply 4 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); electricalexpert65 (2); rasam.syamsudin (1)

Previous in Forum: Power Grid Voltage Fluctuations   Next in Forum: boiler

Advertisement