We are supplying a 6.6kV generator to a power house. I am currently studying my customer single line diagram when i find out something amiss.
The 6.6kV generator is supplying power to a substation and at the substation the voltage is being stepped down to 0.41kV through a transformer of rating ( 6.6/0.41kV 0.63MVA Z = 4.5% )
The power from the transformer is then distributed to the auxillary equipments of the power house through a busbar.
There are 7 load then is connected to the load and the breaker rating for the loads are 400A,160A,100A,400A,630A,630A,160A.
I have done my own calculation of the power needed for the load and is as follows : 1.73 x (400+160+100+400+630+630+160 ) x 410 = 1.76MVA
So , now my question is, if the loads are running at full load, the power drawn will be 1.76MVA. However, the transformer rating is only at 0.63MVA.
Why is the power distribution design this way?
Is this design correct in the 1st place?
Am i missing out some important factors in my calculations?
Would really appreciate if anyone can help me !
Thanks alot !
Confused engineer =(
"Almost" Good Answers: