Air Circuit Breakers

12/29/2009 9:09 AM

HI FRIENDS.......

1.IS AIR CIRCUIT BREAKER IS CONNECTED ONLY IN LV PANELS? CANNOT BE CONNECTED TO SUB-MAIN DISTRIBUTION PANELS ?

2.CAN ACB BE CONNECTED TO CAPACITOR BANK??

3.IF TOTAL LOAD IS 1390KW THEN HOW MUCH IS KVAR? ACB OR MCCB MUST BE USED FOR CAPACITOR BANK?{PLEASE I NEED EXPLAINATION IN DETAIL}

4.WHAT IS FAHU? AN ISOLATOR CAN FEED FAHU?

5.IF FAHU HAVE MUCH LOAD THEN A CONTROL PANEL IS USED.HOWEVER I WOULD LIKE TO KNOW "FAHU HAVE CONDENSING UNITS,SUPPLY FAN,EXTRACT FAN"? AND "MCCB OR ISOLATOR MUST BE REQUIRED TO FEED CONDENSING UNITS,SUPPLY AND EXTRACT FANS?"

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Commentator

Join Date: Sep 2009
Location: INDIA
Posts: 92
#1

Re: Air Circuit Breakers

12/29/2009 10:45 PM

1.ACB can be connected to any panel depends upon load.normally if ur breaker rating is more than 630A ,it will be ACB(AIR CIRCUIT BREAKER),

2 if ur breaker rating is more than 630A it will be ACB for capacitor as wel.

3 to cal KVAR it require ur present P.F and required P.F.For given load it willl be ACB only.

4.FAHU means Fan Air Handling Unit or anything else?It can feed to any load depend upon requirement that what protection u r providing.

5.Isolator is to isolate the supply in overcurrrent or fault condition .u have to replace the fuse after every fault.where as breaker willl trip under fault condition and can be reused again.

Register to Reply
Power-User

Join Date: Aug 2008
Location: East
Posts: 117
Good Answers: 6
#2

Re: Air Circuit Breakers

12/29/2009 11:54 PM

Please switch off caps lock.

Use of ACB is dependent on current rating of feeder. Also sometimes it is client/ owners personal choice. eg some owners are okay with having 1250A MCCBs whereas others want ACB.

ACB can be used for any feeder

for calculating KVARs you need to understand the purpose and then it is a very simple formula

FAHU?

Query 5 is unclear

__________________
Atlas Shrugged - JGD
Register to Reply