Previous in Forum: DC Load banK   Next in Forum: Different Conditions in Which a Surge Divertor is Used ?
Close
Close
Close
6 comments
Rate Comments: Nested
Anonymous Poster

Short circuit calculation

12/31/2009 12:50 AM

How to do the short circuit calculation for transformer.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: Short circuit calculation

12/31/2009 1:20 AM
Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#2

Re: Short circuit calculation

12/31/2009 3:21 AM

A general rule of thumb would be:

Transformer short circuit current =

Transformer Full Load Current / Percentage Impedance of the Transformer

Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#3

Re: Short circuit calculation

12/31/2009 11:16 AM
Reply Score 1 for Good Answer
Commentator

Join Date: Dec 2009
Location: Jakarta 12130 Indonesia
Posts: 76
Good Answers: 1
#4

Re: Short circuit calculation

12/31/2009 9:38 PM

Dear Sir,

I present the simple short-circuit calculation for transformer.

Base MVA = 1 MVA, and Base Voltage = 480V

I base at 480 V =

IB = 1MVA/(

VB = 1 p.u

Assumed there are motors connected on LV system.

IM-RMS = VB/Xm= 1/(0.20) = 5 p.u.

IM-RMS actual = IM-RMS × IB = 5 × 1202 = 6010 Amperes = 6.01 kA.

IM-RMS is zero if there is no any motor operated on this system.

XSC source = (MVA base)/(MVA available) = 1 MVA/500MVA = 0.0020 pu.

XSC network = XT + X Source = .065 + 0.002 = 0.0652 p.u.

I network = 1/(0.0652) = 15.32 p.u

I actual = 15.32 × 1202 A = 18435 A = 18.44 kA.

Fault current at point of fault : I network + IM RMS = 18.44 kA + 6.01 kA = 24.45 kA.

So, 30 kA bus rating selected is meet the requirements.

__________________
RSM Elect Specialist
Reply
Commentator

Join Date: Dec 2009
Location: Jakarta 12130 Indonesia
Posts: 76
Good Answers: 1
#5
In reply to #4

Re: Short circuit calculation

12/31/2009 9:45 PM

Dear Sir,

I am sorry the equation cannot be accepted on this picture, so;

I base at 480 V= [1000000/(√3 x 480)] = 1,202 A.

__________________
RSM Elect Specialist
Reply
Participant

Join Date: Jan 2010
Posts: 4
#6

Re: Short circuit calculation

01/26/2010 4:37 AM

I have a software for short circuit calculation. the software is created myself. you can download from my website

www.shakhawathossain.yolasite.com

Reply
Reply to Forum Thread 6 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

electricalexpert65 (1); lyn (1); rasam.syamsudin (2); shakhawat (1); wareagle (1)

Previous in Forum: DC Load banK   Next in Forum: Different Conditions in Which a Surge Divertor is Used ?

Advertisement