Thanks for the quick replies. Here is more context:
a) I do have the installation manual, and have noted the #8 AWG (up to 125 feet) 90⁰ C wire ... but am trying to make sure I understand the thinking behind this ...
b) The generator sits 60' from the Transfer Switch (Eaton 100 amp model); 40' is buried conduit, 20' is inside walls; with a junction box as the conduit enters the house.
c) The Transfer Switch is fed from the main panel (100 amp 240v breaker); it in turn feeds a 100 amp 240v sub-panel.
Given this ... I had anticipated that the Installation Manual would specify a wire rated at 100 amps.
As I continue to read the manual ... I sense that the generator will produce a maximum of half it's rated capacity on each 'leg' -- hence the two 50-amp circuit breakers in the genset -- so that each power wire only has to support 50 amps (and hence the #8 AWG specification).
I'm just trying to make sure I understand before I run the wires ...