Frequency drives

01/15/2010 9:25 PM

Frequency drives

Had a frequency drive blow a line control 60 amp 3ph fuse panel.

This freq-drive was taken out of service do to upgrade 5years ago.

It was left in the system functioning with no load.

I'm being told a freq-drive that is powered with no load will fail?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#1

Re: Frequency drives

01/16/2010 2:05 AM

No, but if stored for a long time UN-powered, the capacitors can degrade and blow on re-energization.

But any piece of electronics, if left connected (load or no load) for a long time is subject to the normal ravages of electrical grids such as spikes that happen as a natural consequences of modern life; grid switches, utility line capacitors coming on and off, distant lightning strikes etc. Line reactors can provide some benefit in avoiding some of these things but without them, it's entirely possible for a VFD to become damaged to the point of causing fuses to blow.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Score 1 for Good Answer
Guru

Join Date: Oct 2006
Location: Surrey BC Canada
Posts: 1571
Good Answers: 42
#2
In reply to #1

Re: Frequency drives

01/16/2010 11:56 PM

Many VFDs had a design life of 5 to 10 years mtbf for the electrolytic caps.

I am expecting a whole raft of VFDs failures in the near future. Built in obsolescence!

Register to Reply
Anonymous Poster
#3

Re: Frequency drives

01/18/2010 8:44 AM

Correct replys

It is indeed a DC bus capacitor "Dry out" as we call it in our jargon.

There are two remedies avaiable.

for this particuoar drive, replace the capacitors. if drive is under 10HP it is not worth it. If over, maybe, check your cost.

For future, we tipically use a 3 phase variac to gradually (very slow) power the dc bus in no load conditions up to the max voltage allowed for this VFD. Than remove it and rewire to normal fused grid.

semi conductor fuse is recommended on the DC bus before the 6pack transisitors. not all VFD has it installed.

Have a nice day

Joe

Register to Reply
Register to Reply 3 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); GW (1); JRaef (1)

Previous in Forum: replacing Stamford series 4 AVR with SX440 in old Stamford C244B generator   Next in Forum: AC-DC
You might be interested in: DC Motor Drives, Hard Drives

Advertisement