Installing Valves in HVAC Chilled Water Systems

01/20/2010 8:01 AM

In HVAC chilled water system, where is it recomended to install the 2way / 3way valve (i.e in supply line or return line) at AHU / FCUs?

When and where it is advised to install 3way valve in chilled water system?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Anonymous Poster
#1

Re: Installing Valves in HVAC Chilled Water Systems

01/20/2010 10:54 PM

It should be on the return side

Reply
Associate

Join Date: Jan 2010
Location: Charleston, SC
Posts: 25
Good Answers: 1
#2

Re: Installing Valves in HVAC Chilled Water Systems

01/25/2010 12:20 PM

Return side is correct. This is because the pressure in the coil will be higher and prevent air bubbles from getting trapped there. You use a 2 way valve typically for a variable speed pump, and a 3 way valve for constant speed pumps. Even if you had a constant speed pump, you could put a 2 way valve in on a small percentage of FCUs and the pump could ride the curve (and save some money), but you don't want to do too many or the pump could dead head or overheat.

__________________
R. Turner, P.E.
Reply