Dear all,
We are facing a problem in New 66 KV CT during Testing. CT Details as under :
CTR : 600-300/1-1-1 A
Burden : 15/15/-
Accuracy Class : 0.5/5P/PS
ALF/ISF : ≤5/10/-
Types of Defect : Defect observed in Metering Core of Y-Phase CT.
Insulation Resistance : 50000 (+) M Ω in all the CTs.
v Polarity Test : we observed very less positive deflection in Metering Core of Y Phase CT compare to other 2 CTs i.e. R & B Phase.
v Resistance Measurement :
|
Core |
Winding |
R-Phase |
Y-Phase |
B-Phase |
|
Metering |
1S1-1S2 |
2.4 Ω |
0.9 Ω |
2.1 Ω |
|
1S1-1S3 |
4.1 Ω |
0.9 Ω |
4.1 Ω |
|
1S2-1S3 |
2.4 Ω |
0.9 Ω |
2.1 Ω |
|
Protection |
2S1-2S2 |
3.4 Ω |
2.8 Ω |
3.4 Ω |
|
2S1-2S3 |
6.4 Ω |
5.5 Ω |
6.4 Ω |
|
2S2-2S3 |
3.4 Ω |
3.1 Ω |
3.2 Ω |
|
Differential |
3S1-3S2 |
4.2 Ω |
4.2 Ω |
4.1 Ω |
|
3S1-3S3 |
8.6 Ω |
8.2 Ω |
8.6 Ω |
|
3S2-3S3 |
4.5 Ω |
4.5 Ω |
4.5 Ω |
v Ratio Test :
Ø R & B Phase : Result found satisfactory.
Ø Y Phase : Result found satisfactory in Protection & Diff. Core but in Metering Core result is as under :
|
Primary Inject (Amp.) |
Secondary Measured (mA) |
|
300/1 |
600/1 A |
|
10 |
5.52 |
15.39 |
|
15 |
8.29 |
22.86 |
|
20 |
10/65 |
30.30 |
|
25 |
13.11 |
36.67 |
|
30 |
15.39 |
43.0 |
|
35 |
17.38 |
51.5 |
|
40 |
18.84 |
60.0 |
|
45 |
20.14 |
69.5 |
|
50 |
20.36 |
78.2 |
|
55 |
20.36 |
|
60 |
20.36 |
Now any one can help me to find out the problem? Pl. Refer the resistance of CT of Y Phase which is less & equal in all winding compare to R & B phase. Is it possible to short the secondary winding? It is possible to short during transportation?
Now, which type of test should be taken ?
With Regards,
Hiren