Automatic Transfer Switch

01/26/2010 10:12 AM

Dear Gents, what are the differences between the closed transition and open transition automatic transfer switch? also what are the disadvantages and advantages of these ATS's?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
4
Commentator

Join Date: Mar 2009
Location: Southern California
Posts: 97
Good Answers: 15
#1

Re: Automatic Transfer Switch

01/26/2010 11:05 AM

A closed transition switch is also called a make-before-break: the secondary set of contacts closes before the primary set opens, so there is a brief period when both sources are connected to the load (and to each other). Conversely, an open transition switch is a break-before-make: the primary set of contacts opens before the secondary set closes, so there is a brief period when neither source is connected to the load.

If your load is a motor or a light, open transition is fine, since a motor isn't going to suddenly stop turning just because power is removed for a fraction of a second, and lights can flicker without hazard. On the other hand, it could be a problem for an electronic device such as a computer.

However, a closed transition switch is not without its problems: the two sources (primary and secondary) must be in phase or the magic smoke will leak out. If you've got two 480V sources that happen to be 180 degrees out of phase you will be essentially turning one of them into a motor. Stand back and watch the fun. If you want to use a closed-transition switch you must have parallelling gear to ensure that the two sources are in phase.

Register to Reply Good Answer (Score 4)
2
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#2
In reply to #1

Re: Automatic Transfer Switch

01/26/2010 12:31 PM

It is a good answer. I would like to add some more.

For the case of industrial UPS manual transfer switch, the switch must be the Closed Transition (Make-Before-Break). For close transition, there should be a sync-check system which provides the signals of either (or both) 'In Sync' or 'Out of Sync'. This switch should only be operated when the two sources are 'In Sync'. Transfer of the switch at the 'Out of Sync' condition may cause severe damage and safety issue. Generally, a danger sign is recommended to install near to the switch to avoid the wrong operation.

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply Good Answer (Score 2)
Guru

Join Date: Feb 2006
Posts: 1758
Good Answers: 6
#7
In reply to #2

Re: Automatic Transfer Switch

01/27/2010 7:08 AM

Regards.

A GA.

Let me add to your comments on UPS'

I recommend this switch should be a 2-HAND_OPERATED_SWITCH which actually disconnects the Critical-Load from power only then the "Forced-Tranfer" switch can be operated. Both switches are so Interlocked that Power-Transfer switch can not be operated.

Have a fine day !

Register to Reply
Guru

Join Date: Feb 2006
Posts: 1758
Good Answers: 6
#6
In reply to #1

Re: Automatic Transfer Switch

01/27/2010 7:00 AM

A GA for good Answer.

I would like to add that in rotary-MBB-switches there are the type that the rorary contact is extended on the side to keep contact with the previos fixed-conct while making to the next position fixed-contact; & in BBM switches it is very short to ensure that it breaks from the previous fixed point well before it makes to the next fixed contact.

Regards.

Register to Reply
Active Contributor

Join Date: Jan 2010
Posts: 18
#11
In reply to #1

Re: Automatic Transfer Switch

02/03/2010 11:26 AM

Thanks for the information. I have paralleling switchgear with synchronizing panel as well complete with relay protections. I used ASCO paralleling switchgear with redundant master control for the paralleling of the generators. Have you used ASCO paralleling switchgear? Which is better, Zenith Energy Commander by G.E. or ASCO? and why?

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#3

Re: Automatic Transfer Switch

01/26/2010 3:35 PM

There is a BIG difference in application however. Closed Transition ATSs are for parallelling or load sharing, peaking etc. If the ATS is there for emergency backup power, i.e. in the event of a utility power failure, a Closed Transition switch may not only be dangerous, it may be illegal. If the utility power is off, during that brief moment that the switches are all closed the standby generator will be (or trying to be) powering the entire connected grid. This is especially bad if a linesman happens to be working on the utility lines when the ATS closes!

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Score 1 for Good Answer
Guru

Join Date: Feb 2006
Posts: 1758
Good Answers: 6
#8
In reply to #3

Re: Automatic Transfer Switch

01/27/2010 7:17 AM

Regards.

Good comments

In our country I do not know if local Power-stations have any Emergency-Generators to connect to Grids; [some setups have their personal but do not connect to grid].

Linemen keep the keys of of the switch gear feeder on which they are working & put a Shrt-Circuit cables on the power line near their place of work.

Register to Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#4

Re: Automatic Transfer Switch

01/26/2010 4:19 PM

To reinforce what JRaef has said...

The use of a closed tranisition transfer switch in a "classic" emergency power feed setup to provide power to an installation or a part of an installation is not legal in Canada. CEC rule 6-106 talks to this issue.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Commentator
Engineering Fields - Electrical Engineering - New Member India - Member - New Member

Join Date: Dec 2009
Location: Bangalore,India
Posts: 80
Good Answers: 1
#5

Re: Automatic Transfer Switch

01/27/2010 1:42 AM

Dear Mr. Marjohr,

Asco manufactures ATS upto 4000A in ASCO 7000 series. - www.asco.com which is a part of Emerson group. you may please ask their representative. There is 1 more terminology- overlapping neutral. Please confirm whether this is used for closed transition ATS.

Register to Reply
Active Contributor

Join Date: Jan 2010
Posts: 18
#10
In reply to #5

Re: Automatic Transfer Switch

02/03/2010 11:21 AM

Dear Mr. shanbhag,

exactly, I'm planning to use ASCO 7000 series ATS. I have a question, which do you prefer for a 4 pole ATS? a switched neutral ATS or overlapping neutral? what are the difference between these two?

Register to Reply
Anonymous Poster
#12
In reply to #10

Re: Automatic Transfer Switch

02/04/2010 12:25 AM

Dear Mr. Marjohr,

This is the only point where i have a bit of confusion. The fact is that ASCO ATS is a sort of proprietory product(sorry , if am wrong) and since the technicalities of this product is being defined by ASCO, you need to ask their rep only. May be, bothe switched and overlapping may be the same condition, only terminology varies.

ASCO has one more version in ASCO7000 series i.e. with bypass maintenance facility. but it is twice costly compared to normal ATS. Please visit their site www.asco.com or google search emerson power.

Regards

Register to Reply
Active Contributor

Join Date: Jan 2010
Posts: 18
#13
In reply to #12

Re: Automatic Transfer Switch

02/05/2010 8:07 AM

Thank you mr. shabhag. I appreciate your help.

Register to Reply
Active Contributor

Join Date: Jan 2010
Posts: 18
#9

Re: Automatic Transfer Switch

02/03/2010 11:18 AM

Dear Gents,

Thank you for all the information that you gave. I really appreciated it. I prefer to use closed transition ATS since I have a huge critical load to support (IT loads). What I know, closed transition will be operating just like the open transition once the power from the utility fails and transfer to the generators via ATS. The difference between the open and close transition is when if the utility power is back, the closed transition will operate as make before break. it will synch with the utility power before it breaks with the emergency generator power. Is this correct or I misunderstood something?

Register to Reply
Register to Reply 13 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); Haajee (3); JRaef (1); marjohr (4); Mitsurati (1); msamad (1); North of 60 (1); shanbhag (1)