MCCB

01/26/2010 12:09 PM

i work as electrical designer in a project and i would like to know how could i inspire my client to get his approval regarding to use MCCB instead of ACB for rating 400A in outgoing feeder.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#1

Re: MCCB

01/26/2010 12:17 PM

You could start by giving a lot more information. What type circuit? Cost difference?

Reply
Active Contributor

Join Date: Jan 2010
Posts: 10
#9
In reply to #1

Re: MCCB

03/29/2010 2:36 AM

thank you for your interest but i should say that during the meeting i have been aware this is part of mandatory term of contract and there were no choice.

regard

Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#2

Re: MCCB

01/26/2010 3:37 PM

In my opinion, you cannot "inspire" someone to use something that is inappropriate for the application. There is a LOT that goes in to deciding on a Power breaker (i.e. ACB) vs a Distribution Breaker (MCCB). It's rarely a matter of opinion.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply
2
Commentator
Engineering Fields - Electrical Engineering - New Member India - Member - New Member

Join Date: Dec 2009
Location: Bangalore,India
Posts: 80
Good Answers: 1
#3

Re: MCCB

01/27/2010 1:48 AM

Dear Guest,

I am working in Panel manufacturing co and as per my knowledge, All major switchgear manufacturers like ABB, Schneider,Siemens, GE have ratings of ACB starting from 800A.

Now the deciding factor is MCCB or ACB, it depends on load, switching operations, what short circuit it should withstand. Electrical operations, mechanical operations. ACB is superior compared to MCCB in the above cases.

Please refer the data sheets of the above manufacturers (ACB,MCCB) and revert back

Reply Good Answer (Score 2)
Active Contributor

Join Date: Jan 2010
Posts: 10
#6
In reply to #3

Re: MCCB

01/28/2010 7:30 AM

dear sir

thank you in advance for your respond yesterday i held meeting with my client i discuss him the advantage of ACB in complying IEC 60947 regarding to better capability of Ics and having better time discrimination in total final time coordination between incoming ACB abd outgoing MCCB but in our case we have 400A ACB 40KA@1Sec in out going feeder for protecting capacitor.

unfortunately he told me this is our mandatory rule of oil company and you shoul following it up.

Reply
Commentator
Engineering Fields - Electrical Engineering - New Member India - Member - New Member

Join Date: Dec 2009
Location: Bangalore,India
Posts: 80
Good Answers: 1
#7
In reply to #6

Re: MCCB

02/01/2010 12:35 AM

Dear Mr. Alirahnama,

You Have mentioned that this breaker is used for protection of Capacitor feeder. Please give the correct load details. what is the kVAR of Capacitor?

I would wish to tell you that for Power factor correction capacitors, the switching design is a bit different due to the high inrush currents and the overvoltages it produces in the system due to switching and inherent characteristics of the capacitor. when i design the rating of switchgear, take a example: if 100 kVAR capacitor is required, i would multiply it by 2.6 times kVAR value(or sometimes 3 times) to get the current rating of switchgear. Depending on the frequency of switching of capacitors , the decision of ACB or MCCB should be done. As i have earlier said, the ACB is designed for better electrical and mechanical operations and higher Short-circuit current withstand value. and depending on the location and application, type of switchgear is decided. So you customer may be right in considering ACB. of course if you r looking from the cost point of view, you have to take the additional price from the customer.

Reply Score 1 for Good Answer
Power-User

Join Date: Oct 2008
Location: Jakarta Indonesia
Posts: 123
Good Answers: 7
#4

Re: MCCB

01/27/2010 7:31 PM

Dear all,

If the client requires coordination between the 400A feeder and down stream MCCBs, he may requires ACB which can wait the down stream to trip first. MCCB-MCCB coordination is difficult or not possible.

Regards

__________________
Akihito Shigeno @ JGC-Indonesia
Reply
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#5
In reply to #4

Re: MCCB

01/27/2010 8:15 PM

This previous thread may also help: http://cr4.globalspec.com/thread/45169

I would suggest you first get the reasons why your client prefers ACB to MCCB. There may be technical or regulatory or commercial or cultural reasons. Then you can suggest (not inspire) with your reasons for using MCCB. One of the reasons your client prefer ACB for future maintenance facilities.

However, as an engineer, you should be faithful to the client and apply your diligent judgment to propose them whatever you feel well for the client – never propose something that has the interest only for your own side.

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Reply Score 1 for Good Answer
Power-User
India - Member - design engineer Engineering Fields - Electrical Engineering - New Member United Arab Emirates - Member - New Member

Join Date: Feb 2010
Location: dubai,mangalore,bangalore.....
Posts: 145
Good Answers: 8
#8

Re: MCCB

03/23/2010 3:50 AM

i think a mccb would be a good choice if u consider cost factor as it s cheaper than acb and as far as protection s considered it wont dissappoint ur client.....an Acb range starts from 800A in schneider ...so if u want to use it for a 400A then u ll have to use a additional micrologic and set it to trip when current exceeds 400A....this s very costly but highly reliable regarding maintenence and temperature withstanding capacity..........so if ur client is not bothered abt the budget then use acb or else use mccb.....i hope this gives u some hint......

__________________
shamith gambhir, electrical engineer
Reply
Reply to Forum Thread 9 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!