Synchronous Condensers, Anyone?

01/29/2010 10:24 AM

This was posted as a discussion, but got no bites. I'll try it as a question here. This power plant is considering converting a generator to synchronous condenser operation. If anyone has experience with this, I would like to hear about it: challenges, cost, operational issues, maintenance issues, equipment changes, etc. There are 2 large generators (ST prime mover) on the order of 150 mW and one small one (aero derivitive) at about 25 mW. I am dubious of the cost-benefit to this plant since we are not a utility. The location is in a large urban environment. The plant itself is 50 years old. The generators are well-maintained, but no insulation lasts forever. The var load tends to be 15 or 20 mVARs lagging when generating, so I assume a synchronous condenser would run that much leading. Heating issues? Thanks.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Active Contributor

Join Date: Jan 2010
Posts: 10
#1

Re: Synchronous Condensers, Anyone?

01/30/2010 12:08 AM

We are highly experimented 35 Year experience in Power plant with similar problem -

You understand that resolve a problem for a 150MW/e ,you may not help Remotely .

Joshua Gabriel SAADA

Engineer consultant.

Alternative Power Systems
http://www.aps-microgen.com
http://www.calnetixps.com/
www.CalnetixPS.com
Joshua@aps-microgen.com
saadaj@netvision.net.il
Alternativepowersystems@gmail.com
Tel: 972(0) 88652424
972(0) 774100494
Cell: 972(0) 546566191
Tel/fax on demand: 972(0) 88652424
Electrical Test Engineer: License Nr: 085195
Senior Electrical license Nr: 007922

Register to Reply
Guru

Join Date: Aug 2007
Location: Indiana, USA
Posts: 579
Good Answers: 61
#2

Re: Synchronous Condensers, Anyone?

02/01/2010 10:18 AM

If the generators are designed for synchronous condenser operation, you should not have a problem on that end. If they are not designed for it, you need to look at the capacity and % regulation of the exciter and voltage regulator. You may not be able to provide enough excitation, or you may get an unstable output. You will also need to change your protective relay settings for the new operating design.

On the turbine end, the steam turbines will have issue with end-stage heating. If not already installed you may need to add an exhaust hood spray system. The aero will have issues with blade erosion and poor combustion at low loads, but both should be manageable with forethought and proper maintenance.

Economically, I can't see this project making much sense. The steam turbines are too large for the your VAR loading, and combustion turbines are deathly expensive in most parts of the world. You need to take a good hard look at the available revenues, especially whether or not you would have a guaranteed long-term income, before making any decisions.

__________________
Experience: The knowledge you gain just AFTER you needed it.
Register to Reply
Power-User

Join Date: Oct 2008
Location: Meherrin Virginia
Posts: 319
Good Answers: 6
#3

Re: Synchronous Condensers, Anyone?

02/01/2010 10:25 AM

How do you plan on getting this unit on line? If you simply run it to line speed and lock the control valves at the no load condition you may have problems with windage heating in the turbine stages.

The only way I have seen it accomplished was with two units specifically designed for the function, they had disconnect couplings and thrust bearings at the generator. The idea being to tie them together electrically on gear with one of them disconnected from the turbine, they would be tied to the system electrically as a pair. The driving unit could be used for load or taken off the line, the other could have the field varied to accomplish the synchronous condenser operation. These units were 1920' vintage.

My only comment on the economics would be that if you have the capability to improve power factor why wouldn't the power company pay for the benefit. They don't have too many qualms about charging for the effect.

__________________
If you fail to follow through, you will fail.
Register to Reply
Guru

Join Date: Aug 2007
Location: Indiana, USA
Posts: 579
Good Answers: 61
#4
In reply to #3

Re: Synchronous Condensers, Anyone?

02/03/2010 9:25 AM

If the plant is located in an industrial or dense urban area, it might make sense. Unless he's in a dense load center, the conductors on the poles would not be large enough to transmit that much reactive current to where it's needed.

We have 2 steam units (1965 & 1975) which are designed to be used as generators or sync condensers, and I've run them in both modes with no problem. We don't use them as condensers anymore because the nearby factories have all shut down, and it's cheaper to use line compensators where the new load on my system is located.

__________________
Experience: The knowledge you gain just AFTER you needed it.
Register to Reply
Member

Join Date: Jun 2009
Location: San Diego, CA, USA
Posts: 8
Good Answers: 1
#5
In reply to #4

Re: Synchronous Condensers, Anyone?

02/03/2010 11:13 AM

A little more information on my plant: there are 2 active units in an urban area with shipyards about 2 miles away. There is a 69/138 kV sub owned by the local utility. There are 2 active 69 lines and 3 active 138 lines.

Do your units use clutches? Can you use one as a condenser and the other as a generator? Are there other means of spinning up the generator besides a steam turbine? What kind of exciter is used? How about var control, AVR, stabilization, etc.?

Thanks for your comments.

Register to Reply
Guru

Join Date: Aug 2007
Location: Indiana, USA
Posts: 579
Good Answers: 61
#6
In reply to #5

Re: Synchronous Condensers, Anyone?

02/03/2010 1:25 PM

Mine are both direct-drive, 3,600 RPM, GE synchronous generators, rated 50MW & 25MW. No clutches or gearing are involved, and the attached turbines (1 each) are the only source of rotation. The primary design is to provide real power (MW), with the condenser function simply an extra rating.

The static exciter/voltage regulators are GE SCT-PPT systems (Saturable Core Transformer with Power Potential Transformer), which was the standard for GE's marine turbine division up until the late '80's. I learned the same system in the Navy many years before. VAR control on mine is completely manual, based on the AVR setting. They are not designed to follow power factor, but rather for "base load" VAR compensation, so stability is not really an issue. The exciters are somewhat over-engineered, but I don't know if that's for the sync. condenser or just a consequence of designing a system before computer-assisted design was readily available.

If the utility has significant VAR load passing through the 69/138 sub, you might be able to convince them that you are a better deal than static compensation on the HV lines. If they have to transport it significant distance, the line losses will make your proposal less attractive. I get similar proposals about every other year (I am the utility here), and so far no one has presented an attractive enough package for me to sign on. However, your location and direct access to transmission may make your proposal very attractive. The utility will look at a) need (do they need that much VAR support?), b) relative cost to meet the need, and c) safety and reliability. Safety/reliability is a deal-breaker, but they won't bother to look there unless the economics work.

If you have no intention of using either unit as a MW generator again, I'd simply uncouple them from the turbines and connect an induction motor with belt & clutch to get up to speed. Your existing AVR's may or may not work, depending on the limitations of design. You will need to have PF-following or VAR setpoint capability, which may not be available on the existing units. Basler has a very nice line of relatively inexpensive AVR's which may suit your needs.

__________________
Experience: The knowledge you gain just AFTER you needed it.
Register to Reply Score 1 for Good Answer
Power-User

Join Date: Oct 2008
Location: Meherrin Virginia
Posts: 319
Good Answers: 6
#7

Re: Synchronous Condensers, Anyone?

02/03/2010 5:42 PM

If you are in the situation that you intend to perform the double function of making power and operating in synchronous condenser mode, You should contact the OEM to ascertain if there is in fact a windage heating problem. If there is a problem it can probably be overcome with some simplistic resolution such as a properly placed line with a shut off valve and an orifice of the proper design. I don't think the amount of cooling steam involved would cause a concern with overspeed. Of course "trying this at home, unassisted" is strongly discouraged.

__________________
If you fail to follow through, you will fail.
Register to Reply
Register to Reply 7 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Joshua Gabriel SAADA (1); Kurt Alderson (1); otha (2); pwr2thepeople (3)