instruments earthing

01/31/2010 8:35 AM

am new in this field and i want to know what is the theory for connecting the cables shield from one side only

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: El Lago, Texas, USA
Posts: 2639
Good Answers: 65
#1

Re: instruments earthing

01/31/2010 10:35 AM

The reason for connecting cable shields on one side only is to avoid ground loops. Since the shield is connected to ground, and the cable usually contains signals that have their own ground returns, connecting the cable shield on both ends makes two separate ground connections, and you can get loop currents.

Reply
Power-User
South Africa - Member -

Join Date: Nov 2008
Location: Johannesburg
Posts: 295
Good Answers: 12
#2

Re: instruments earthing

02/01/2010 12:27 AM

Hi there,

Just to add to the points mentioned above.

We do not earth the screen on both sides in instrinsic safe loops either as the screen could induce stray voltages etc into the signal line, which would then make the IS loop unsafe.

Earthing the screen on one side is also a form if lightning protection.

Regards,

Craig