Capacitor Size for Old Single-Phase Motor

02/09/2010 9:17 PM

Unit heater fan motor, probably early 1950's, in large manufacturing facility receiving new tenants in space formerly vacant for a few years.

Motor nameplate data: Baldor (manufacturer), Baltric Line, Specification 6-1014-993, 3/4HP, 115/230V, 11.6/5.8A, 840 RPM, 60Hz, Class A, 1.0 Service Factor, Code E, rating 55-degC, Series 6 (might be 61).

Motor seriously overheated some time in the past; rewind shop reported that the heat damage made the winding data very difficult to obtain. Rewind shop received motor without any capacitor; returned it with 15-mfd size. Fan is cast aluminum blade (about 36" dia) with large heavy hub; mounted on motor shaft. Rewind shop says manufacturer could not find any data for motor. Fan takes 33 seconds to come to speed with 24-25A starting current and about 9% voltage drop during starting (dropping from 124 to 114VAC); running current 12.0A. With paralleled 20mfd capacitor, it takes 25 seconds to come to speed; running current is 12.6A. Rewind was using magnet wire with class-H insulation.

Can anybody tell me the factory specification for the motor's capacitor? If not, can anybody tell me how to calculate the proper size capacitor? Or, is it largely empirical? Is there something else I have missed?

Thanks--JMM

Register to Reply
Pathfinder Tags: capacitor motor
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#1

Re: Capacitor size for old 1-phase motor

02/10/2010 1:52 PM

Can anybody tell me the factory specification for the motor's capacitor? If not, can anybody tell me how to calculate the proper size capacitor? Or, is it largely empirical? Is there something else I have missed?

15uF sounds about right for a 3/4 hp single phase capacitor run motor (capacitor size isn't to critical and capacitor selection is the same for currently sold single phase motors), your fan startup speed does not however.

Based on the excessively high startup time and high starting and normal operating currents it sounds like the fan motor is overloaded. Possible causes are - Faulty or mis-wired start winding, motor bearing issue or other mechanical issue preventing motor turning freely, motor is too small for application.

Since this is only a small fan motor (inexpensive and not application critical) it may be time to buy a new motor (especially if the rewound start winding can not be replicated), least you waste more money on a motor that is just too old to repair economically.

__________________
jack of all trades
Register to Reply
Guru

Join Date: Jul 2006
Location: Eastern Kansas USA
Posts: 1503
Good Answers: 128
#2
In reply to #1

Re: Capacitor size for old 1-phase motor

02/10/2010 2:19 PM

j-o-a-t,

Thanks for the reply. I suspect that the combination of 115V winding with 840 RPM (8-pole) is a real killer for finding a new motor. That is probably why the old one was rewound. Considering that the rewind shop said they had a lot of trouble in reading the winding data from the old motor, it is quite possible that there is a winding problem as you have hinted. Friends in another rewind shop where I worked years ago suggested that the capacitor size may have to be substantially increased.

Thanks-JMM

Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#3
In reply to #2

Re: Capacitor size for old 1-phase motor

02/10/2010 5:59 PM

Friends in another rewind shop where I worked years ago suggested that the capacitor size may have to be substantially increased.

While capacitor size isn't too critical, increasing the capacitor size excessively can have a detrimental effect on the life of the motor (and the capacitor).

Don't forget you may have the option of changing to a similar (but more commonly available) motor such as a single phase 6 pole (faster) motor, 110/220V winding, or even switching to a three phase 8 pole motor. It depends on your application of course (but in the end it is still just a fan).

__________________
jack of all trades
Register to Reply
Guru

Join Date: Apr 2007
Location: Hyderabad, India
Posts: 596
Good Answers: 12
#4

Re: Capacitor Size for Old Single-Phase Motor

02/10/2010 11:07 PM

Is it a capacitor start & capacitor-run motor or capacitor start and run motor? Check it got any centrifugal switch. If you find switch then capacitor value will be around 80MFD and if not 4MFD.

__________________
Subramanyam
Register to Reply
Active Contributor

Join Date: Feb 2010
Posts: 14
#5

Re: Capacitor Size for Old Single-Phase Motor

02/11/2010 12:41 AM

11.8 mfd capacitor will solve your problem

Register to Reply
Commentator

Join Date: Mar 2009
Location: Georgia mountains
Posts: 64
#6

Re: Capacitor Size for Old Single-Phase Motor

02/11/2010 11:04 AM

Why is everyone assuming that the magnet wire and the capacitor value are for 120vac? Maybe the long startup is due to undervoltage. Was it designed to operate on 230 vac?

Luther M

__________________
There are old pilots and there are bold pilots, but there are no old bold pilots.
Register to Reply
Anonymous Poster
#7

Re: Capacitor Size for Old Single-Phase Motor

02/11/2010 11:55 AM

This is madness! A 55-60 year old unit heater has done its job. Buy a new one. Modern unit heaters run at a minimum 80% efficiency ( there are condensing models that run as high as 93%). Add spark ignition, lighter weight, more CFM, etc, etc, to the list of features. As the saying goes: Let's work smarter.

Register to Reply Off Topic (Score 5)
Power-User

Join Date: Feb 2010
Posts: 268
#8

Re: Capacitor Size for Old Single-Phase Motor

02/11/2010 12:57 PM

http://www.amazon.co.uk/Electric-Motors-Home-Workshop-Practice/dp/1854861336 this book is all you are gonna need.

__________________
guds777
Register to Reply
Guru

Join Date: Jul 2006
Location: Eastern Kansas USA
Posts: 1503
Good Answers: 128
#9

Re: Capacitor Size for Old Single-Phase Motor

02/12/2010 10:40 AM

Friends,

I appreciate the range of comments and suggestions.

To Kvsubramanyam: It is a permanent split capacitor type of motor, not capacitor start and capacitor run. There was and is no centrifugal switch. The motor terminal box is on the side of the motor, not in an end-bell; it has 4 leads only. No terminals or ability to change direction.

To Jack Of All Trades: The incoming power there was and is 115V/1-phase. Any change to that would require running a new circuit from the distribution panel, etc. Using a faster motor (6-pole) would require the use of a matching blade, etc. The location is near the ceiling of a fairly tall manufacturing facility just inside a tall roll-up door for truck entry/exit. The heater has a live steam coil for supplying the heat, so the immediate environment can be quite hot when the fan is off (most of the time). Therefore, I doubt that a belt drive from a 4-pole or 6-pole motor would survive. I appreciate the warning about life-span if a too-large capacitor is used.

To Luther M: I quoted the original nameplate data on the thread's original post. The motor was rewound for this 115/230 voltage.

To Guest (rated off-topic): This particular unit heater is used as an air curtain, and sees intermittent use. I would agree with your comments about ignition systems for gas fed appliances. However, all the unit heaters in this facility (over 100) use steam through heat exchange coils. Your comment has merit, but does not apply here.

To all: The problem appears to be a too low starting torque. The motor rewind shop said it started OK by itself. They did not have the fan blade with the motor, so did not test the motor with its actual load. The facilities maintenance manager has the option of asking the mechanical contractor to return the motor and fan blade to the motor rewind shop so they could test the combination and perhaps improve it. I don't know if this will happen. This manager is fully aware of my concerns about the startup time, etc. (and is generally a pretty level-headed and reasonable person; far from "just-a-penny-pincher").

Thanks--John M.