How to Control Transformer Loss

02/10/2010 6:02 AM

our factory transformer idely consume 3 kw consume per hr 3 unit .how to minimize the losses.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Anonymous Poster
#1

Re: how to control transformer loss

02/10/2010 8:40 AM

What is the rating of the transformer?

Any transformer will have its efficiency (and hence the no load losses).

If it is abnormal, change the transformer.

If it is normal, switch off the incoming feeder when idle.

Register to Reply
Member

Join Date: Oct 2008
Posts: 7
#3
In reply to #1

Re: how to control transformer loss

02/13/2010 4:48 AM

transformer Rating :11kv/440v,500kva,delta/star conn.

which side current transformer connect?

Ht structure to transfomer cable distance 100 mtrs.cable rating 185 Sqm.xlpe.

how to minimize cable loss?

Register to Reply
Anonymous Poster
#4
In reply to #3

Re: how to control transformer loss

02/13/2010 7:33 AM

For a 500KVA transformer a 3KW loss looks to be very good.

The input current is only about 26A

for 185sqmm (sqm ) XLPE cable, your resistance is about 0.17 Ω/km ie for your ampereage the total loss in cable will be about 35W

You are well within all normal practices (unless I have miscalculated something) including the 3KW.

Where is actually the problem? Amd I missing something?

Register to Reply
Associate

Join Date: Oct 2006
Location: Hyderabad,India
Posts: 49
#2

Re: how to control transformer loss

02/10/2010 11:19 AM

Dear Sir

1)As asked by one of the participant ,let us knw the rating of the transformer.

2)The losses of the transformers and their prices are linked.Higher the loss, lower is the price.At the time of procurement itself ,it needs to be taken care.

regards

Register to Reply Score 1 for Good Answer
Register to Reply 4 comments