Sizing a Neutral Conductor

02/10/2010 3:42 PM

How do you size the neutral conductor of a wye grounded transformer?

__________________
Thank you for your help - By far the best info site!
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Commentator

Join Date: Jan 2010
Posts: 70
Good Answers: 4
#1

Re: Sizing a Neutral Conductor

02/10/2010 4:39 PM

What is the max possible current that can eventually flow through such a grounding wire. Double it, then size the wire.

Register to Reply
Commentator

Join Date: Sep 2009
Location: Singapore
Posts: 77
Good Answers: 1
#2

Re: Sizing a Neutral Conductor

02/10/2010 10:28 PM

Determine the following:

1. Line to ground fault that will flow to the neutral conductor.

2. Time to Clear the fault

3. Conductor temp and Short circuit temp.

then use the formula below as per NFPA 70.

Register to Reply
Commentator

Join Date: Sep 2009
Location: Singapore
Posts: 77
Good Answers: 1
#3

Re: Sizing a Neutral Conductor

02/10/2010 10:31 PM

Det. the ff:

1. Line to ground fault that will flow to the neutral conductor.

2. Time to clear the fault.

3. Temp of conductor and SHort circuit.

then us the formula below as per NFPA 70/

Register to Reply Score 1 for Good Answer
Power-User

Join Date: Sep 2009
Location: Houston, TX
Posts: 118
#4

Re: Sizing a Neutral Conductor

02/10/2010 10:37 PM

Thanks for everyones help however I had hoped to read a thread from NEC that simply states (from tables), how to size a neutral wire that is used for grounding and not a current carrying conductor. Since the neutral is grounded and the ground grid is connected accordingly it would appear that they would be the same!

__________________
Thank you for your help - By far the best info site!
Register to Reply
Commentator

Join Date: Sep 2009
Location: Singapore
Posts: 77
Good Answers: 1
#5

Re: Sizing a Neutral Conductor

02/11/2010 3:17 AM

Check this book for Grounding Grid calculation ( IEEE 80 guide for safety in AC substation grounding 2000. )

Register to Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#6

Re: Sizing a Neutral Conductor

02/11/2010 9:17 AM

First off... you are using language that is rather confusing. Are you looking to size the "neutral conductor" or the "grounding conductor". They are not the same thing.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Power-User

Join Date: Sep 2009
Location: Houston, TX
Posts: 118
#7
In reply to #6

Re: Sizing a Neutral Conductor

02/11/2010 9:32 AM

I designed switchgear for compressor stations. The customer had me install a ground bus and a neutral bus and connect them both to ground. System voltage is 480 v, 3 phase. He specified a 300 amp ground bus and a 1200 amp neutral bus. The circuit breaker is rated at 1200 amp LTP. He required a surge suppressor as well. Makes no sense to me why he would have a ground bus and a neutral bus but he does. The ground bus is tied into his grounding grid. I'm not much on NEC rules as I don't use them much and thought there would be a NEC table that would simply state the ground/neutral size relative to the current carrying conductor size.

__________________
Thank you for your help - By far the best info site!
Register to Reply
Register to Reply 7 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Alexander M. Berlin (1); jonald (3); jraubsr (2); North of 60 (1)

Previous in Forum: Fractional Pitch Windings   Next in Forum: Estimated KW for a Dried Fruit Factory

Advertisement