Static and Dynamic Motor Starting

02/10/2010 11:36 PM

Dear Sirs,

1. When do we use Static and Dynamic motor starting?

2. What is the difference between the two?

3. Can we evaluate the system using Static only not dynamic?

Thank you very much.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#1

Re: Static and Dynamic Motor Starting

02/11/2010 9:07 AM

I have never heard these terms before. Could you mean "Star" and "Delta" motor starting?

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
4
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#2
In reply to #1

Re: Static and Dynamic Motor Starting

02/11/2010 11:19 AM

I think you are talking about the study of the electrical system for motor starting in ETAP (or any such software). Here are the answers:

1. When do we use Static and Dynamic motor starting?

If you know the Motor torque characteristics, Load torque characteristics and the inertia information of the motors, bearings and loads, you can do the Dynamic motor starting study. Otherwise, do the Static motor starting study - it simply needs the starting time and the locked rotor current of the motor.

2. What is the difference between the two?

(1) The Dynamic motor starting develops the motor starting current characteristics based on the motor starting torque, load torque and the inertia, while the starting current remains flat at locked rotor current during the starting time for Static acceleration. (See the previous posting http://cr4.globalspec.com/thread/42981 , comment # 2 for detail how the starting time is calculated for Dynamic acceleration).

(2) Dynamic starting acceleration requires additional data than the Static acceleration.

(3) The Dynamic acceleration calculates the acceleration time and current from the input data, while the Static acceleration assumes you know the starting time and current.

(4) For Dynamic acceleration, the starting current is not 100% flat during the starting time, but in Static acceleration it is flat.

(5) Static acceleration is simple, Dynamic acceleration is rather complicated.

3. Can we evaluate the system using Static only not dynamic?

Yes. Make sure you have the correct information for motor locked rotor current and the stating time for the load.

Go the ETAP tutorial site (http://www.etap.com/training/tutorials-training-videos.htm) and see the tutorial #12 (Dynamic Acceleration) and #13 (Static acceleration).

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply Good Answer (Score 4)
Active Contributor

Join Date: Jun 2014
Posts: 18
#4
In reply to #2

Re: Static and Dynamic Motor Starting

06/26/2014 10:56 AM


Very good explanation,
Was usefull for me too,thanks!

Register to Reply
Commentator

Join Date: Sep 2009
Location: Singapore
Posts: 77
Good Answers: 1
#3

Re: Static and Dynamic Motor Starting

02/11/2010 7:07 PM

Thank you very much.

Register to Reply
Register to Reply 4 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

jonald (1); Morgan_fer (1); msamad (1); North of 60 (1)

Previous in Forum: CT Polarity Tests   Next in Forum: Mobile Test Kit for Electrical Cables

Advertisement