Anonymous Poster

Ferranti Effect

02/12/2010 11:54 AM

Sir,

we are receiving higher voltage than sending voltage from substation please let me know is this due to under ground cable?or due to over head transmission line or due to both?

over head transmission distance :35 kilo meter(100 MM AAA CONDUCTOR)

UNDER GROUND CABLE:200 METERS(3X300 SQ.MM,XLPE)

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Anonymous Poster
#1

Re: ferranti effect

02/12/2010 12:13 PM

How much more?

Reply
Participant

Join Date: Feb 2010
Posts: 1
#2
In reply to #1

Re: ferranti effect

02/12/2010 12:31 PM

approximately 1.5 Kv

Reply
3
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#3
In reply to #2

Re: ferranti effect

02/12/2010 1:13 PM

The answer is (1) both 35 KM overhead line and underground cable or (2) only the 35 KM overhead transmission line. This is based on which side of the transmission line the cable is located.

(1) Normally the capacitive charging current for cable is more than the overhead line. So, if the cable is located at the load end side, the charging current drawn by the cable is passing though the overhead line and it is causing more negative voltage drop (voltage increase effect) in the overhead line. In this case, both overhead line and underground cable are causing this Ferranti effect.

(2) If the cable is located at the supply end, the charging current drawn by the cable is not passing through the long transmission overhead line and so the cable has negligible effect to the Ferranti effect. So, in this case mostly the 35 KM overhead line is contributing the voltage increase effect.

This effect will be eliminated once you have load at the receiving end.

See the links for more clarification:

http://tkne.net/downloads/power/transmissionlines1/transmission%20lines/_Ferranti%20Effect.pdf

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Reply Good Answer (Score 3)
Anonymous Poster
#4

Re: Ferranti Effect

10/14/2010 4:31 AM

The ferranti effect occurs only in long overhead transmission lines under no load or light load conditions.

Reply
Anonymous Poster
#5

Re: Ferranti Effect

10/24/2010 11:39 PM

http://transmissiondesignhub.blogspot.com/2010/10/ferranti-effect.html

Reply
Reply to Forum Thread 5 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

Anonymous Poster (3); msamad (1); SAISRUJI (1)

Previous in Forum: Cable Meggar Values   Next in Forum: Electrical Engineering
You might be interested in: Cable Laying Services, Cable Assemblies, Cable Trays

Advertisement