Meter

02/22/2010 5:33 PM

Here is what I would like to do, I have a work shop three hundred ft. from my house, about 25 year ago I ran power from my house to the shop, I used double o aluminum from a 100 amp breaker in the main box, I have now installed Geo heat in the house and I would like to install a meter in the basement of the house between the main box and the wire going to my shop so I can tell how much usage is being used at the shop and how much at the house. I do not want to get the power co. involved. My question is what type of meter can I buy at a elect. supply house that will do the trick. Thanks.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Jun 2009
Location: South of Minot North Dakota
Posts: 8376
Good Answers: 775
#1

Re: Meter

02/22/2010 7:14 PM

All you need is a standard issue Kilowatt Hour meter like the utilities use on your home service. They are common on eBay and sell for around $15 - $40 depending on brand and current capacity. You will also need a socket box for it as well and that should be around $20 - $40 as well.

If you have basic electrical skills you could probibly install it yourself too. They are just a four wire hookup ,two in and two out.

Register to Reply Score 1 for Good Answer
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#2

Re: Meter

02/23/2010 8:13 AM

Just a slight caveat to tcmtech's statement. I bought one of the inexpensive meters and it is great! It measure lots of parameters.

Kill-o-Watt is the name. (Just for reference, not an endorsement.)

But, it's only rated for 15 amps. Maybe the more expensive ones have a higher capacity. Just a thought.

Good Luck.

Register to Reply
Guru

Join Date: May 2006
Location: Placerville, CA (38° 45N, 120° 47'W)
Posts: 6215
Good Answers: 248
#3

Re: Meter

02/24/2010 1:36 AM

I used to have a kiloWatt-hour meter like tcm referred to and there were no issues using it.

You DO know to turn off power while installing it, don't you?

The one issue might be the kind of connections - there are special procedures and connectors for aluminum wire. We wouldn't want a fire!

__________________
Teaching is a great experience, but there is no better teacher than experience.
Register to Reply Score 1 for Good Answer
Guru

Join Date: May 2006
Location: Placerville, CA (38° 45N, 120° 47'W)
Posts: 6215
Good Answers: 248
#9
In reply to #3

Re: Meter

02/25/2010 10:32 AM

I decided to add a few more details. I obtained the kwh meter I had from an old house that was being torn down. If I recall correctly, it only had a capacity of something like 30 Amps, which was perfect for my purpose. At the time, I was teaching science and physics. I mounted the unit on an L-shaped plywood stand, and added a standard (3-wire) 120V plug to the input, and a standard 120V socket to the output. Ground went directly to the aluminum case of the meter. Line and neutral went to the input, and the output went to line and neutral of the socket.

I regularly loaned the assembly to students, and they got extra credit for measuring the energy consumption of home appliances (usually refrigerators or TVs). I never had any problems with it. When I first set it up, I had a student whose father was with the county department of weights and measures, and he calibrated it for me for free. When I retired from teaching 15 years ago, I gave the unit to another teacher.

Good luck with your project! Dick

__________________
Teaching is a great experience, but there is no better teacher than experience.
Register to Reply
2
Commentator

Join Date: Nov 2007
Location: Third Rock from the Sun (?)
Posts: 76
Good Answers: 8
#4

Re: Meter

02/24/2010 7:41 AM

Hello Folks, Just another caveat to tcmtech; it is not just two in and two out. At the minimum you will have a hot leg, a neutral and a ground wire. That is what is known as a two-wire service (120V). Add a second hot leg for a three wire service (120/240V) and now you have four in and three out of the meter box. Which brings up the big question. Do you have a 240V service or a 120V service to your shop? The person previous was correct in that different sized boxes have different prices. I would recommend not less than a 100 amp box as they are easier to get than 30A and 60A plus the meters will always fit. When you are buying the meter be sure you get either a 2 or 3 wire meter, whichever meets your needs. When you are at Home Depot picking up the material be sure to get a squeeze bottle of a corrosion inhibitor to coat your aluminiumn conductors with. If you don't use it the connectors may only last for 15 to 20 years; but it really does cut down on the resistance of the connection. You'll probably need a set of hex wrenches but it sounds like you are the guy that I would borrow tools from. A small wire brush, welder's slag brush is just fine, will work to brush the conductors just prior to shoving them down in the bottle of inhibitor. BTW, I like to take the top off of the squeeze bottle and shove the skinned end of the conductor down in the goo, it is less messy that way. And like another contributor said, be darn sure the power is off; before starting this project you will also need to put your hands in your pockets, put your brain in gear, and study the thing out. Be safe and enjoy your shop - - afterall -- the original quote was that a man's shop is his castle.

__________________
vagabond
Register to Reply Good Answer (Score 2)
Power-User

Join Date: Oct 2007
Posts: 397
Good Answers: 3
#5

Re: Meter

02/24/2010 9:12 AM

All good info from the repliers. However, depending where You live, It would be just as easy and cost effective to install a meter at your shop and have a drop put in. Power company will not charge for putting drop in and You will have the advantage of a seperate power supply for Your shop. I did this and have no regrets.

oilcan13

Register to Reply Score 1 for Good Answer
Associate

Join Date: Jan 2009
Posts: 47
Good Answers: 1
#7
In reply to #5

Re: Meter

02/24/2010 3:23 PM

If I add another service or drop, they will put me on a commercial rate. No thanks to that.

Register to Reply
Associate

Join Date: Nov 2007
Posts: 50
#8
In reply to #5

Re: Meter

02/25/2010 8:36 AM

The problem with having the electric company add the meter and drop is you now have 2 bills (2 minimum payments + usage). Where I live the power company considers any additional meter to be commercial and higher rates apply. It may be different where the original poster lives, but I'd check with the power company before making any decision.

Register to Reply
Guru

Join Date: Jun 2009
Location: South of Minot North Dakota
Posts: 8376
Good Answers: 775
#6

Re: Meter

02/24/2010 1:02 PM

Depending on what type of meter you find the surplus single phase two circuit utility type meters are usually a standard 4 line connection assuming you are American or have the two line 120/240 volt American service system of course. The meters themselves come in everything from 20 amp to 400 amp capacity ranges so just look for one rated equal to or greater than what your supply is capable of. 200 amp rated are usually the most common ones to find.

The second supply system from the utility company usually has a second meter and service fee attached to it. Depending on where you live that convenience could end up setting you back $20 - $50 a month just for being connected before you ever used a single KWH. That alone rather justifies sub metering your shop if the lines are already in place.

Register to Reply
Register to Reply 9 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

digger104 (1); dkwarner (2); lyn (1); NoEngr (1); oilcan13 (1); tcmtech (2); vagabond (1)