Transformer Calculations

02/23/2010 4:48 PM

I have the primary and secondary kV, the kVA and the impedance. How would I calculate the X/R? I didn't see the X/R listed on the transformer.

thanks.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Anonymous Poster
#1

Re: Transformer Calculations

02/23/2010 4:49 PM

The primary voltage is 480, secondary is 120. kVA = 15 and Impedance is 4.4%. Sorry forgot to include that.

Regards.

Reply
Commentator
India - Member - New Member Engineering Fields - Electrical Engineering - New Member Technical Fields - Technical Writing - New Member

Join Date: Feb 2010
Location: India
Posts: 92
Good Answers: 2
#3
In reply to #1

Re: Transformer Calculations

02/25/2010 10:40 AM

As per IEEE standards and Table No-1.2, X/R ratio=0.867 when %Z=2.7789

In this case, %Z=4.4,

so X/R= 0.867*4.4/2.7789= 1.373

Reply
Anonymous Poster
#2

Re: Transformer Calculations

02/24/2010 6:01 AM

Ask Manufacturer-

only he can supply this (else test at your place)

The other option is refer the IEEE std 242 which will give the recommended value of it for different ratings (same as ANSI C57)

And last, most approximate is a thumbrule about 4.9

Reply