Magnetic VFD and Motor Overload

03/09/2010 2:24 PM

We are running a Magnatec Vfd and suddenly we are having all kinds of faults. Mostly overtorque of motor overload. The drive shows the motor drawing 25% more amps than normal. We have had the drive checked out by a repair shop and they see nothing wrong with it. We changed out the motor-same problem. We Jog the machine by hand-smooth. Any ideas what could be causing the problem
?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#1

Re: Magnetic VFD and Motor Overload

03/09/2010 4:16 PM

Have you checked the VFD parameter settings to see if anything has been accidentally (or intentially)b changed?

Also check the VFD fault history record to see if the drive captured any fault events that may shed some light on what could be causing the problem. It may be something simple.

__________________
jack of all trades
Register to Reply
Guru
Panama - Member - New Member Hobbies - CNC - New Member Engineering Fields - Marine Engineering - New Member Engineering Fields - Retired Engineers / Mentors - New Member

Join Date: Dec 2006
Location: Panama
Posts: 4273
Good Answers: 213
#2

Re: Magnetic VFD and Motor Overload

03/09/2010 11:02 PM

What are you driving with this motor? You could have some sort of blockage in the system being driven that is causing an actual motor overload, rather than a problem with the VFD...

Register to Reply
2
Power-User

Join Date: Jul 2008
Location: UK
Posts: 205
Good Answers: 50
#3

Re: Magnetic VFD and Motor Overload

03/10/2010 5:55 AM

Hello Tucker,

A few points come to mind

Overload or 'overtorque' (software calc) can be caused by:

1. Mechanical overload ( I assume it isn't)

2. Single phasing motor supply (is the 3 phase current balanced at near zero Amps with UVW in the clamp only - possible bad connection or faulty output from VFD)

3. Overvolting the windings - most common. Check motor connection voltage rating for applied frequency, set VFD parameters accordingly. What is your mains supply compared to motor rating, some VFD's are set by default to put out voltage at set frequency at the supplied input voltage. If your supply is 480 and the motor 440 this would explain it.

4. Torque miscalculation by very incorrect motor data entered into VFD.

5. Faulty current detection, compare the VFD to your clamp readings. Is the motor getting hot??

Please confirm your motor nameplate details, your supply details, appliued output voltage and Hz from VFD and then this may be explained more easily (hopefully). As always, a better description of your application and any relevant history will assist in any help suggestions.

Hope this helps to eliminate some possibilities....

__________________
Something new every day!
Register to Reply Good Answer (Score 2)
Anonymous Poster
#4

Re: Magnetic VFD and Motor Overload

03/10/2010 9:23 AM

We too have a few Magnatec drives in our facility and experienced something similar a couple of times (but not as extreme) with one driving a 150 hp motor running a fan.

Case 1: An internal wiring issue with the motor (plus according to the re-winding shop, a bearing issue even though the shaft rotated with no discernable - to the hand - problem).

Case 2: Current loads were higher than normal and the motor, fan bearings (via sound analysis during operation), and general process all checked out fine. There were no other local error codes except the overload condition. A few days after a couple of "nuisance" trips, one of the control boards burned out. Still not sure if the cooling fan went out or if there was blockage in the cooling vents but the system was apparently overheating to the point of causing an intermittent failure mode. The drive that we had was obsolete and we upgraded the electronics - which took a different set of parameters for set-up, including a different nesting order in the program. Have you recently changed out the drive and if so (and to one of the earlier posting points) are you sure the setup parameters are correct?

Is this a new installation and does it occur on start-up, during steady state operation, or ramping during process changes? When we changed from a mechanical damper control to the vfd, we had to limit the rate of startup to eliminate overamping of the motor and we also limited the rate at which the mortor would speed up when adjusted from the vfd to avoid "shocking" the system.

Register to Reply
Commentator

Join Date: Mar 2009
Location: Georgia mountains
Posts: 64
#5

Re: Magnetic VFD and Motor Overload

03/11/2010 9:32 AM

Tucker,

Check that the supply voltages are stable and that the motor leads are not leaky. The driven load can cause the motor to lag enough to be reflected in the 25% higher motor currents indicated. If it is not an electrical problem, it is mechanical. Look into the driven mechanism what has changed?

Luther M

__________________
There are old pilots and there are bold pilots, but there are no old bold pilots.
Register to Reply
Register to Reply 5 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); cwarner7_11 (1); jack of all trades (1); Luther M (1); MalcolmK (1)

Previous in Forum: Rotor Windings and Slip Ring Motors   Next in Forum: Calculations for Motor-Driven Generators

Advertisement