Thermocouple Compensation Wires

03/19/2010 12:32 PM

what is the difference between compensation wire and extension wire

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User

Join Date: Mar 2010
Posts: 132
Good Answers: 7
#1

Re: thermocouple compensation wires

03/19/2010 1:44 PM

Compensation wire is wire that is used in a thermocouple from the point of sensing to the point of cold junction compensation (cjc end) where the signal is measured.

Extension grade wire is only used to extend a thermocouple signal from a probe back to the instrument reading the signal. The extension grade wire typically will have a lower ambient temperature limit in which the wire may be used. Namely, it may pass a signal representing a higher temperature as received from the probe, but the wire physically may not be exposed to higher temperatures. Thermocouple wire may be used as extension wire, but extension grade wire may not be used in the sensing point (or probe part) of the thermocouple. Part numbers for extension wire typically begin with an "EX" prefix.

Good luck!