Restraining Current

03/19/2010 2:35 PM

PL. expline about the restraining current, when we do the transformer stability test we get the following datas.

transformer 40MVA, 66KV/11KV ,Yd1, CT HV side 400/1 , LV side 2500/1A. we give 403V AC on primary side and we short the secondry after the CT. The readings are Pr.current is 11.5,11.3,11.4A and secondry current is 71.6,70.9,70.6A.

When we saw the differencial relay display(Micom) the restraining current is 0.030,0.030,0.030A.

PL.let me know how i calculate this current ,

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User

Join Date: Mar 2010
Posts: 105
#1

Re: Restraining Current

03/19/2010 3:37 PM

Ibias = (I1+I2)/2 for MICOM P642 or P643.