Why an AVR should be kept in manual mode if the the load on the generator is less than 25%.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Commentator
India - Member - New Member Engineering Fields - Electrical Engineering - New Member Technical Fields - Technical Writing - New Member

Join Date: Dec 2009
Location: India
Posts: 68
Good Answers: 4
#1

Re: AVR - Manual Mode and Generator Load

03/21/2010 11:24 PM

Please let us know the Make & Rating of the Alternator..

In the case of Big MW HV Generators the Responce of the AVR to the Low Load Conditions is Poor.

e.g Assume that the Generator requires the Excitation Current of @ 15 Amp at Full Load, It will Require less than 1/4th of the Full Load Excitation Current at 25 % Load, If the AVR is Designed to Deliver the Excitation Current of 1.4 Times the Full Load Excitation Current @ 21 Amps DC, then the Excitation current Required at 25 % Load will be Less than 3 Amps, For AVR it is difficult to manage this Low Excitation Current, Hence Manual Mode of Operations.

I have seen similar kind of AVRs for LT Alternators as well.