Anonymous Poster

current transformer

03/28/2010 6:12 AM

Dear All,

My CT is 230 kv, 1600/1 A, 5P20.

Please can you tell me, what is the saturating current of that CT.

Thanks,

Rashid

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Anonymous Poster
#1

Re: current transformer

03/28/2010 8:16 AM

20 times 1600A........!!!

Reply
Commentator

Join Date: Dec 2009
Location: Mangalore, India
Posts: 65
Good Answers: 4
#2

Re: current transformer

03/28/2010 12:56 PM

This CT can safely carry a current upto 32kA (1600 X 20) without getting saturated, provided the CT burden is well within the rated burden. If not, the CT may saturate for a current less than 32kA.

Reply
2
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#3
In reply to #2

Re: current transformer

03/28/2010 6:55 PM

'CT saturation' and 'CT accuracy limit factor' are different things.

For 1600/1A, 5P20 CT, the number 20 is called the 'accuracy limit factor' which means the CT composite error will remain within 5% with 20 x 1600 A = 32 kA primary current. With more than 32 kA, the error limit will be more than 5% but actual saturation may occur higher than 32 kA and the CT class designation (5P20) doesn't have the saturation limit information. The saturation current can be obtained from CT excitation curve.

And off course, the CT burden must be within the CT VA rating. As 'Electronaut' mentioned the CT saturation may occur less than 32 kA if the burden exceeds the rated VA.

See also

http://cr4.globalspec.com/thread/43440

https://w3.energy.siemens.com/cms/00000032/aune/Documents/EA/08_CT%20Dimensioning.pdf

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Reply Good Answer (Score 2)