NACE Requirement

03/28/2010 10:26 PM

Hi,

NACE Certification for material is required when Process fluid contains sulfur or it is corrosive in nature. But i don't know how much sulfur amount is required in process so i can tag it with NACE Requirement ? Please let me know a minimum amount of sulfur in fluid for which NACE is must.

Regards,

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User

Join Date: Nov 2009
Posts: 335
Good Answers: 63
#1

Re: NACE Requirement

03/28/2010 11:32 PM

The Jamesbury document here:

http://info2.jamesbury.com/requests/download/downloaddoc.aspx?docid=T101-4

goes through an example of determining the mol%H2S. Good reading!

Register to Reply
Member

Join Date: Nov 2009
Posts: 5
Good Answers: 1
#3
In reply to #1

Re: NACE Requirement

03/29/2010 2:25 AM

Hi Carl E,

Thanks ... Informative document....

Register to Reply
Anonymous Poster
#2

Re: NACE Requirement

03/29/2010 1:54 AM

"NACE Requirement" is too vague.

As per NACE MR0103-2007:

1.3.5.1 Some environmental conditions known to cause SSC are those containing an aqueous phase and:

(a) >50 ppmw total sulfide content in the aqueous phase; or

(b) 1 ppmw total sulfide content in the aqueous phase and pH <4; or

(c) 1 ppmw total sulfide content and 20 ppmw free cyanide in the aqueous phase, and pH >7.6;

(d) > 0.3 kPa absolute (0.05 psia) partial pressure H2S in the gas phase associated with the aqueous phase of a process.

1.3.5.1.1 The high-pH sour environments differentiate refinery sour service from the oil and gas production sour environments covered by NACE MR0175/ISO 15156, because many wet sour streams in production also contain carbon dioxide and hence exhibit a lower pH. Another major difference is that chloride ion concentrations tend to be significantly lower in refinery sour services than in oil production sour services.