Variable Frequency Drives

04/10/2010 3:22 PM

Hi, this is very unusual but interesting to know that power system is affected due to VFDs and EMI is a major concern for installations in the area. I have come across one such recurring problem of ELR tripping at source main switch Board for no apparent fault. Monitorinng over time and increasing leakage current and time setting to 0.5 Amp/ 1 second no real earth fault was found but most likely it is related with crane operation which is found without any surge suppression at input .Would any one advise further action to eliminate this problem. Will it be aggravating problem incase two identical cranes with adjustable frequency Drives are connected to draw power from common busbar. It will be very Kind in case you share your observations with such machines and affect on 415 volts system. Thanks in advance.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Active Contributor

Join Date: Aug 2009
Location: India
Posts: 12
#1

Re: Variable Frequency drives

04/10/2010 8:05 PM

VFD's used in common busbar systems should have second environment filters so as to reduce the current harmonics in to the system. Using a lower pulse inverter (generally 6 pulse) will cause such problems. It is recommended to use a higher pulse PWM (12 or more).

We have similar problem in our industry with ABB drives ACS 800 without second environment filters. Solutions are available for these problems, but not economical. We are also looking for economic solutions.

You can do a engineering change, by shifting your non VFD feeders to another bus bar. (Simple and best mehtod) if possible.

__________________
Mind is like a parachute, no use if you do not open it
Register to Reply Score 1 for Good Answer
Power-User
India - Member - design engineer Engineering Fields - Electrical Engineering - New Member United Arab Emirates - Member - New Member

Join Date: Feb 2010
Location: dubai,mangalore,bangalore.....
Posts: 145
Good Answers: 8
#2

Re: Variable Frequency Drives

04/12/2010 6:59 AM

i think the vfd in your case generates harmonics which will heat up the neutral wire and cause the elr to trip.........is ur vfd compatible wit yo motor (technical ratings?).......does yo vfd have emc filters inbuilt? is ur motor rating compatible wit the load driven by the motor?....vfds can be connected in a common bus, it jus depends on the load which s driven by the motor.....usually for small loads they can be connected to a common bus bar, i don know whether it s applicable for very large loads.......

__________________
shamith gambhir, electrical engineer
Register to Reply
Anonymous Poster
#3

Re: Variable Frequency Drives

04/13/2010 7:47 AM

Installing a 1 to 1 ratio transformer from line to VFD will eliminate some or most of the problems by serving as a choke to suppress most of the noise generated by the VFD.

Try it.It works .

HTRN

Register to Reply
Register to Reply 3 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); imandi007 (1); SHAMITHGAMBHIR1 (1)

Previous in Forum: DC Motor/Alternators   Next in Forum: Transformer Question

Advertisement